Configure Group I/Os with .cm file
  • Andi_33
  • February 22, 2024 at 10:05 AM
  • Andi_33
    Hello everyone,
    currently i am trying to create a .cm file to auto configure my Group I/Os. I think i have a pretty good idea on how to do it but i am missing 1 essential information. I would like to use the "KCL SET VAR" command to set the SYS vars of the Group I/Os RACK, SLOT, START PT and NUM PTS but i dont know where to find them. Has anyone an idea how these sys vars are called. Or mabye there is a better way to perform this configuration in a .cm file, like a specific command or something.
    Thanks for help
  • Go to Best Answer
  • hoitzing
    24
    128
    • February 22, 2024 at 1:40 PM
    I'm not aware of any system variables that can be set for the port configuration, but afaik there are two options:
    1) Load a DIOCFGSV file containing the desired IO configuration, I would expect this can be done using a *.CM file
    2) Use a KAREL program with the built-in function SET_PORT_ASG that you can RUN with a KCL command
    Sidenote, when looking into the ASCII version of DIOCFGSV.VA, this is just a list of variables in 'program'/namespace/... [MDIO_MAIN]. This makes me wonder if it's possible to 'KCL SET VAR' on these variables to directly change port configurations from a *.CM file. If the other two options aren't quite what you need it might be worth checking out
  • EnergyAddict
    45
    133
    • March 6, 2024 at 2:05 PM
    • Best Answer
    I picked this command out of another thread, and through trial and error I think I've got it somewhat figured out. "DIOASG # # # # # # #" is a CM file command.
    Below is my understanding not anything I've been able to find documentation on, however it matches similarly to the KAREL Command SET_PORT_ASG:
    EDITTING as I learn more.
    DIOASG Io_Type Range_Begin Range_Length Rack Slot Io_Type Start_Point
    • Io_Type: This determines whether you are assigning Digital Inputs, Digital outputs, UOPs, etc. It seems to follow the numbers from KLIOTYPS.KL (see THIS thread).
    • Range_Begin : Starting index of the IO that you are configuring
    • Range_Length: Number of sequential IO indices to configure
    • Rack: Physical location of the IO board/module
    • Slot: Space on the rack where the IO is connected
    • Io_Type: I don't really understand what this is supposed to be, but making it the same as the first number seems to work, Unless you want to "Clear" the IO assignment, then 0 seems to work.
    • Start_Point: Starting point within the Rack/Slot
    The Code below Configures some Digital IO:
    SPEP_OFF
    !Clears Current DIO Configuration
    DIOASG 1 1 512 0 1 0 1
    DIOASG 2 1 512 0 1 0 1
    !DI[1]-DI[128] Configured to PLC Rack
    DIOASG 1 1 128 89 1 1 1
    !DI[301]-DI[310] Configured to DCS CPCs
    DIOASG 1 301 10 36 6 1 1
    !DO[1]-DO[128] Configured to PLC Rack
    DIOASG 2 1 128 89 1 2 1
    !DO[301]-DO[310] Configured to DCS NSIs
    DIOASG 2 301 10 36 0 2 1
    SPEP_ON
    Group inputs/outputs work with the same command but with a slight Adjustment:
    DIOASG Io_Type GI_GO_# Range_Length Rack Slot Io_Type Start_Point
    • Io_Type: Group Inputs are 18, Group Outputs are 19
    • GI_GO_#: Seems to be the GIO[#] that you are configuring
    • Range_Length: Number of IO indices to configure to the GI
    • Io_Type: I don't really understand what this is supposed to be, but making it the same as the first number seems to work, Unless you want to "Clear" the IO assignment, then 0 seems to work. UOP assignments seem to need to point at your digital IO.
    • Start_Point: It looks like this is the Starting point within the Rack/Slot
    SPEP_OFF
    !Clears Current GIO Config for lines 1 through 5
    DIOASG 18 1 0 0 1 0 1
    DIOASG 18 2 0 0 1 0 1
    DIOASG 18 3 0 0 1 0 1
    DIOASG 18 4 0 0 1 0 1
    DIOASG 18 5 0 0 1 0 1
    DIOASG 19 1 0 0 1 0 1
    DIOASG 19 2 0 0 1 0 1
    DIOASG 19 3 0 0 1 0 1
    DIOASG 19 4 0 0 1 0 1
    DIOASG 19 5 0 0 1 0 1
    !Configure GI[1] to inputs 1-8 from a PLC
    DIOASG 18 1 8 89 1 18 1
    !Configure GI[2] to inputs 9-16 from a PLC
    DIOASG 18 2 8 89 1 18 9
    !Configure GO[1] to inputs 1-8 from a PLC
    DIOASG 19 1 8 89 1 19 1
    !Configure GO[2] to inputs 9-16 from a PLC
    DIOASG 19 2 8 89 1 19 9
    SPEP_ON
    Note the SPEP_OFF Command seems necessary at the top.
    I've tested all of this only in Roboguide, not on an actual robot yet, but it seems ok so far.
  • Group Output
  • Group Input
  • .cm