Obtaining a D series controller (not sure if it is a 40 or 42).It is currently configured for 480V input Per the Kawasaki label, which was an option in the D series spec sheet. I see a reference to a transformer, is it possible to wire this unit (Presumably without the transformer) and run it on 240V 3 phase?
Kawasaki D Series controller power requirement
-
Waterproof -
November 20, 2023 at 7:08 PM -
Thread is Unresolved
-
-
SkyeFire
November 20, 2023 at 7:13 PM Approved the thread. -
According to specs sheets I have for FS06L, if you have a European D40 controller (as attached).
With a requirement of 5.9KVA with a source of between 380vac and 440vac.
Some things need to be considered:
1. KVA requirement, can this be provided by a lower three phase source.
2. The primary of the mains transformer supplies the following secondary supplies:
a. 26vac to supply brakes.
b. 210vac - 230vac to supply AVR (Low voltage power supply.
c. 210vac - 230vac to supply Single phase outlet (if required).
d. 210vac - 230vac three phase to supply the power electronics (MC Unit and Power block source).
No idea if this can be done as I have never cut and shut any controllers outside of the supplied conditions, so good luck if you can manage it.