1. use menu config>IO>autoexternal and change input for move enable to 1025
2. fan need to be replaced from time to time, this is consumable item. in short term check that it is not seized. if it does not run fast enough, you will get this message. this fan is accessible from the back side of the cabinet - it is behind the grill.
3. batteries are another consumable item and need to be replaced. they are inside cabinet. depending on KRC edition, they may be on the inside of the door, or in the lower left corner under the air duct etc. 2pcs of 12V 5Ah SLA batteries with larger style terminals (F2).
4. and 5. Devecenet slave that is configured in WorkVisual is not reachable. it is not powered up or it is disconnected. if this node is no longer available, use WorkVisual to remove it from configuration. as always make backup(s) before you touch anything