I am working on setting up a used robot at work. It’s a R-30ib controller. I have figured out where to wire the inputs to start remotely however when I make more than one input at once they all come on. Does anybody know how to correct this issue?
I had the same issue...You have two or more inputs wired they all come on correct?
I am using the CRMA15 I/O. This is what the book says
SDICOM1 to 3 signal are common selection signal for SDI.
When +24F common is used, connect to 0V.
When 0V common is used, connect to +24F.
SDICOM1 Selects a common for DI101 to DI108.
SDICOM2 Selects a common for DI109 to DI120
If you're using +24F you need to attach the SDICOM 1-3 to 0V
See the note: SDICOM1 is for Inputs 101-108 etc.
Hope this helps. Now I am asking for help.
How did you wire an external start?
I cannot get an external button perform the Cycle Start.