I am working on setting up a used robot at work. It’s a R-30ib controller. I have figured out where to wire the inputs to start remotely however when I make more than one input at once they all come on. Does anybody know how to correct this issue?
Fanuc UI Inputs
-
TheCraigofCraigs -
May 19, 2022 at 11:53 PM -
Thread is Unresolved
-
-
panic mode
May 20, 2022 at 2:56 AM Moved the thread from forum General Discussion of Industrial Robots Only to forum Fanuc Robot Forum. -
Correct wiring.
-
I was able to fix the first problem. Now I am having an issue with a INTP-206 (Interface 3) digital fault. Anyone have any ideas I can’t find anything useful online or in manual
-
Your program is trying to deal with IO that isn't defined.
-
TH
I could be much much easier for us to give you an answer if you post your UI/UO config
-
Thanks everyone it was an old job that needed deleted.
-
I am working on setting up a used robot at work. It’s a R-30ib controller. I have figured out where to wire the inputs to start remotely however when I make more than one input at once they all come on. Does anybody know how to correct this issue?
I had the same issue...You have two or more inputs wired they all come on correct?
I am using the CRMA15 I/O. This is what the book says
SDICOM1 to 3 signal are common selection signal for SDI.
When +24F common is used, connect to 0V.
When 0V common is used, connect to +24F.
SDICOM1 Selects a common for DI101 to DI108.
SDICOM2 Selects a common for DI109 to DI120If you're using +24F you need to attach the SDICOM 1-3 to 0V
See the note: SDICOM1 is for Inputs 101-108 etc.
Hope this helps. Now I am asking for help.
How did you wire an external start?
I cannot get an external button perform the Cycle Start.