Please, does somebody have experience using Wenglor câmeras with FANUC Robots? I am trying to communicate a Wenglor Smart camera in a R30iB controller, using Ethernet IP. I need to know if it´s necessary to add diagnostic data in the total of IOs - if yes, how much Input and Output bytes.
Wenglor cameras
-
emitiekan -
April 1, 2017 at 1:59 AM -
Thread is marked as Resolved.
-
-
try to read it from the EDS file
-
Some time ago I have connected the laser distance sensor from Wenglor to the R-30iB over EthernetIP. Unfortunately, Fanuc assistance was needed, as it was necessary to change some system variables (unavailable in the standard configuration menu on the TP), the values came from the Rockwell's RSLinx software...
-