Hi! We have some serious problem with this communication. On C5G we have on the B&R X20IF10D3-1 EtherNet/IP adapter (slave). We already done the IO_CNFG and IO Map on controller side 32+32 Bytes. On OMRON side we have imported the .EDS (device description file) of the EtherNet/IP adapter and configured it. When we try to download the network configuration we get this error... any ideas... no solution since now from B&R or COMAU...
ETHERNET/IP CONNECTION OMRON PLC C5G CONTROLLER
-
IlFincoITA -
January 21, 2016 at 7:59 AM -
Thread is marked as Resolved.
-
-
Hi! Solved this morning. We antered into B&R device at low level to see if .EDS file has the same "VendID" ad other stuff. Found different values. We manually edited the .EDS file with hardware values and solved...