repaired cpu after disaster loaded all software back in and cant find the section to look and change it to work with 455 welder anolog v 4.21-1
seems to be working as general mig and i need alu pulse to work
has anyone set one up before?
thansk tom
repaired cpu after disaster loaded all software back in and cant find the section to look and change it to work with 455 welder anolog v 4.21-1
seems to be working as general mig and i need alu pulse to work
has anyone set one up before?
thansk tom
zarmock: set up the R-J2 as Lincoln + PW450. The analog interface box takes care of signal emulation. The robot is non-the-wiser that is is communicating to a digital machine. Than you can use the toggle switches on the front of the machine to setup for Al pulse / gas / wire size etc.
is this done in control start or in setup ?
Yes from a controlled start. Once setup as Lincon PW450 start cold. Then make sure your IO is configured. Some of it becomes uninitialized.