  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 30, 2024 at 1:48 PM

    Hi DS186

    Thank you for the assistance with that. It works!!!


    I had to also change the update time and increase the watchdog to 150ms for some reason to get it to work, but it works fine now.

  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 30, 2024 at 12:53 PM

    This is the profinet safety on the robot controller

    Images

    • image1 .jpg
      • 181.08 kB
      • 1,360 × 1,200
      • 27
  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 30, 2024 at 12:52 PM

    Hi here they are as requested

    Images

    • TIA.png
      • 263.43 kB
      • 1,828 × 1,275
      • 34
    • robot.jpg
      • 141.25 kB
      • 1,095 × 1,200
      • 31
  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 30, 2024 at 11:42 AM

    Thank you for that, for some reason I had a blindspot and did not see attachments.

    So my fanuc device is up and running, the F_iPar_CRC matches on the robot profisafe interface. I can also send and receive normal IO. The only issue the safety module does not want to reintegrate. I have seen however that my QBAD is still on, and as far as I know the QBAD signal must go off first before the module can be reintegrated.

    With my reintegration logic, all I am doing is triggering my ACK_REI input on my F-I/O data block like I normaly do with other safety devices.

    Images

    • Screenshot.png
      • 229.77 kB
      • 1,922 × 558
      • 22
  • Problem configuring PROFISafe for RB30+ controller with CP1604 card

    • Morne Ferreira
    • July 30, 2024 at 9:33 AM

    Can you please then send me the manual for the CP as well?

  • Problem configuring PROFISafe for RB30+ controller with CP1604 card

    • Morne Ferreira
    • July 30, 2024 at 9:24 AM

    Hi

    I am having issues reintegrating the profinet device on my PLC, I am however using the S536 Profisafe and not the CP.

    Is there any guides on how to do reintegration on teh S536 board?

  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 29, 2024 at 2:39 PM

    I found the issue I was having, on the Siemens side I chose the 8 byte profisafe module, as the pendent was saying that we are using 8 bytes. It ended up being the 1 byte profisafe module on the PLC.

    I am using the A05B-2600-S536 card with the J931 option.

    The issue I am having now is the constant SRVO-0419 error even though the F-iPar_CRC Matches.

    On the plc I get the following error:

    Substitute values are output for the F-I/O.
    User acknowledgment at the ACK_REI tag of the F-I/O DB is required for the re-integration of the affected F-I/O to eliminate the (error) causes.
    Check the PROFIBUS DP/PROFINET IO connection and ensure that there are no external interference sources.
    Check the parameter assignment of the F-I/O in the hardware and network editor. If necessary, set a higher value for the F-monitoring time.
    You can obtain more information by searching for the event ID in the STEP 7 online help.

    Now I have triggered the ACK_REI tag but it does not do anything to the alarm.

    I cannot upload any images as the website wants a URL to the image and not the image itself.

  • SRVO - 419 PROFisafe comm error 1,1

    • Morne Ferreira
    • July 26, 2024 at 11:45 AM

    I have a similar issue, also getting the SRVO-419 error, but on my plc the safety module in slot one says Input/output data not available. With the standard Icon of 0101. The normal IO slots in slot 2 to 5 work fine and I can send data across from plc to robot, but the safety does not want to recognize it at all.

    I have checked firmware versions, gsdml versions and all the F_iPar_CRC match, it just does not send it through to the robot. On the robot side the F-iPar_CRC received shows NO 0

Advertising from our partners

IRBCAM
Robotics Channel
Robotics Training
Advertise in robotics
Advertise in Robotics
Advertise in Robotics
  1. Privacy Policy
  2. Legal Notice
Powered by WoltLab Suite™
As a registered Member:
* You will see no Google advertising
* You can translate posts into your local language
* You can ask questions or help the community with your knowledge
* You can thank the authors for their help
* You can receive notifications of replies or new topics on request
* We do not sell your data - we promise

JOIN OUR GREAT ROBOTICS COMMUNITY.
Don’t have an account yet? Register yourself now and be a part of our community!
Register Yourself Lost Password
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on Google Play
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on the App Store
Download