Hi guys, my problem is solved,
The problem was that I did not have the safety network number and safety input and output size correctly put in the section of EIP CIP-Safety Operation.
It has been to change size and generate safety number in the RSLogix and pass it to the Fanuc to start working correctly. Thanks all
. -
Thank all for replying.
In the adapter configuration I have the same size of inputs and outputs (10words)
The mapping of digital inputs and outputs i think i have it correctly addressed, i have linked the digital inputs [1-160] with rack 89, slot 1 (PLC), start 1 and status is ACTIV. Same for digital outputs. -
Hello, is a my first post, so be gents pelase.
I have problems with the ethernet / IP connection between a fanuc r30i and allen-bradley logic5572s . In the robot I have configured the PLC as ADP and I can ping correctly.
The strange thing is that if I force an output in the robot, the PLC sees it, instead, the robot does not see the signals that the PLC sends.
Can anybody me??