yes its cheap .but fails frequently .I checked all but fan fails .For temporarily any bypass fan option so only ask.
Posts by Anandhakrishnan
-
-
FSAL-G2:A1 SRVO-135 FSAL alarm (FAN MOTOR ISSUE)
How to disable the fan in R30IA ?
(FOR TEMP PURPOSE)Any disable option .
R30IA CONTROLLER , DC 24V 3 WIRE -(RED ,BLACK ,WHITE) MMB-MAT 1608KL-05W-B39
kindly support -
WE SWAP R30IA 2000 TO R30IB 2000 ... ITS OK NO ISSUE
-
DEAR SIR,
WE HAVE AROUND 50 ABB ROBOT (IRC-5 CONTROLLER & IRB 6640 ROBOT)
CURRENTLY
WE ARE USING ONLY OIL ANALYZER.
OTHER THAN THAT
IF ANY ANALYZING OR INSPECTION TOOL (PDM) AVAILABLE ??????
IF AVAILABLE ,KINDLY SHARE THE DETAILS .....PLZThank you ..
-
DEAR SIR,
WE HAVE AROUND 200 FANUC ROBOT (R-30 IA & B) CONTROLLER & R 2000-IB ROBOT)
CURRENTLY
WE ARE USING ONLY GREASE ANALYZER.
OTHER THAN THAT
IF ANY ANALYZING OR INSPECTION TOOL (PDM) AVAILABLE ??????
KINDLY SHARE THE DETAILS .....PLZThank you ..
-
-
Dear friends,
we changed ABB IRB6640 robot 5 & 6th axis gear & motor ,after replaced offset happened 1.5mm to 2.5 mm ,after change calibrate & fine calibration done but its not ok ....if any other solution available ,,,pls share ....
I tried edit motor offset value (new motor offset value ) also ,but it is not solved .... -
After finish the image backup restore ,quick mastering done .thats enough .suppose quick matering not happended means just check the master count value & ref count value in system variable .
suspected problems are,
1.pulse mismatch .
2.Robot not mastered
3.Robot move without calibration . -
-
-
-
required for system building ...
check the robot studio version
And install robot studio in laptop
later required for controller key & Drive key to update in robot studio system building procedure .
YOU HAVE THE PROCEDURE FOR SYSTEM REBUILD ????
If you don't have the proceduremail me
anandhakrishnanb@ymail.com -
-
Here this alarm came SERVO-018 Brake abnormal FAULT .i follow the below procedure Action-3 Solve this issue .but i checked the brake connector & cable everything normal .but how servo amplifier failure
An excessive brake current is detected. The ALM LED on the servo amplifier is lit.
(Action 1) Check the cables and motor brakes connected to CRR88 connector on the servo
amplifier.
If a short-circuit or grounding fault is found, replace the failed part.
(Action 2) Check the cables and motor brakes connected to CRR65A, CRR65B connector on
the servo amplifier. If a short-circuit or grounding fault is found, replace the failed
part.
(Action 3) Replace the servo amplifier.how servo amplifier failure what is the cause???
-
-
PRIO-608 I/O MISMATCH FAULT.In that time error one shot in i/o controller to reset.If any other way to solve the issue.
-
In FANUC robot 2000 IB profinet fault displayed after power OFF/ON .. PNIO profinet fault & robot I/O mismatch .In that time we doing like this
Menu -> Profinet -> I/O device-> Error one short -> Enable/Disable->Enable then reset the error .ok
Any solution to solve this problem permanently