I was just referring to this reply. Sorry people, once the power has been lost to a Fanuc pulse coder, the pulse counts that were stored in the variable master count are useless. It needs to be remastered
Posts by joyojukwu
-
-
what is the difference between I tried to reload the SYSMAST.SV file in controlled start and then set the master done to true, then calibrate. And it didn't work, and Once the batteries go dead this is your only option. The pulse coder reference is lost; this is what the batteries backup! Line up the witness marks, master, and calibrate the robot, touch up your programs and back up your controller
-
Hi Guys Is it possible for someone to delete robot mastering from the pendent or is lost from control power? Also, where is the mastering stored?