Hello,
We recently bought a KUKA INZ55/5 390-00207-0 FE201 69001124 safety card, but the card is missing the X924 connector in the top right. Would anyone know where to find a replacement connector that we can repair this with? Online searches for the connector have proven nearly impossible, given the variety of connectors on the market.
-
Thank you, panic. We're going to try using a DMM as you suggest and see if anything pops out as the problem. If not, I'll respond here again, if that's OK.
Greatly appreciate your assistance on this, hopefully we can get up and running.
-
So, K14 and K9 should be on at all times? Because we have been able to operate with just K9 on at times, but when K14 is on and K9 is off, it doesn't work either.
-
We have a KRC1 system that has been in operation for over 20 years, but recently we have been having problems with the drives disabling for no apparent reason, and mostly with no error messages besides "drives not enabled". When looking at the FE201 safety card, if relay #9 is lit and relay #14 is off, the drives seem to work fine. But whenever the opposite is true, something is stopping the drives from enabling in automatic mode. We can't tell if it's a problem with the Beckhoff modules, the MFC, the DSEAT, or the FE201, or something else.
Any help or places to start here would be greatly appreciated, as our company relies on this machine quite heavily. I've noticed many posts on here asking for log files - if those are needed, can someone advise how we can download those and provide them?
Thanks for your time!