    Hello Panic I search for this older beckhoff DTMs in Download section but i didn't find it, is this still available?

    Hello to everyone.


    - KRC4 KSS 8.2.18


    I'm facing an issue with NEW devices of beckhoff, EL6752 (devicenet slave), when we replace it, the led status MNS keep blinking and the network doesn't work.


    At the menu on smartpad, I/O Devices, when we click on reconfigure the module worked after that, but if I reboot the robot we have to make this procedure again.


    I changed this module other times and never had any issue before.


    I'm suspected about the revision number in module 6752.


    Has anyone ever face this issue?

    Hello. Search for the file "C:\KRC\SmartHMI\SmartHMI.exe.Standard". In this file all the HMI is defined. Then in this file search for line "<SoftkeyBar SystemName="SKB_STOP_NORMAL" Aliases="SKB_STOP_PARENT, SKB_STOP_CHILD, SKB_STOP_FOLD">" and under this line there will be buttons defined like button 1, button 2, ... search for button 5 and add the parameter Right="UM20" at the end of the line.
    "<Button Position="5" DBKey="TPBaseTouch" ProcID="2500" ModuleIdent="INLINEFORM" ProcParam="0" Right="UM20"/>. Now you have defined user level to that button. So when operator will be logged in the touchup wil be disabled, when Expert user will log on the Touchup button will be active. Then do a cold boot with reload files.


    You can use this approach for other buttons like for delete, new, ...


    I haven't tested yet what happens if technology package like arctech or any other is installed which adds the lines into this file(does the lock stays or not).

    Just for report that's works for me

    Tks a lot!!