Show screenshots of the other tabs of the generic module setup.
We have it working. One of our technicians discovered that if we used slot 10 instead of slot 1 like the manuals say and the way our other forty robots are programmed it now works.
SO instead of configuring our DIO as 89-1-1 we now have 89-10-1 and under the ethernet IP we have connection #1 as false and connection #10 as true. It now communicates with the PLC instead of giving me incorrect size errors. I am not sure why slot 10 works and not slot1. Makes no sense.