    Fanuc Irvision can come with a black/white or a color camera, your choice. Often you can still distinguish color with the black/white camera, but depends how close the colors are to each other.


    Sent from my SM-G930V using Tapatalk

    Yes this a bug with Fanuc software when doing offline programming. The compiler that converts from 'ls' to 'tp' doesn't allow it. My suggestion is to change it to another UT that has not been taught so it will have the same coordinates as UT:0.


    UT:0 only works if you are programming from the teach pendant so if you are doing a mix of online and offline programming, it is a best practice to not use UT:0 at all.

    My preference is option 2. A machine may require many other devices and in my experience they integrate better with the PLC as a master. Modern PLCs are also much easier to structure data than using robot registers.


    Sent from my SM-G930V using Tapatalk

    Try setting the IO auto configuration system variable to 1.


    $IO_AUTO_CFG


    Then power cycle the controller. You may need to clear out the DI/O config first for it to auto detect what is connected.

    You may need to change the system variables $SCR.$RUNOVLIM and $SCR.$JOGOVLIM


    Runovlimit is for running a program in Teach mode, Jogovlim is for jogging in teach mode


    Default is 50%, you can change it to 100% but may get occasionally T1 speed faults. 90% is pretty reliable.

    Some variables that are write protected need to be changed in a Controlled Start.


    becncor21's option is also a good way to go that may be simpler than the System Monitor. You would create an AutoStart program with no motion or you could use the Run statement to start your RO fault program as soon as the main program starts.

    T1 speed exceeds the safe speed for T1 mode.


    Slow down your override % when in T1. Usually 90% is reliable to eliminate the speed spikes that trip this alarm.


    Sent from my SM-G930V using Tapatalk

    Check your wiring on the EE connector. Are you intentionally using the hand broken signal (hbkn) or is their a loose or wrong connected wire?


    Sent from my SM-G930V using Tapatalk

    I would check it with a voltmeter before I power off. Also, write down the current joint angles.


    Sent from my SM-G930V using Tapatalk

    I have a tool that can find recursion. If you send me a backup I could test it for you. Must be an "all of the above" backup.


    Sent from my SM-G930V using Tapatalk

    DCS is the Fanuc name. Each robot mfg will have a a different name for their safety software. Under the latest RIA I believe they call it Safety rated soft axis limits or something to that effect.


    Sent from my SM-G930V using Tapatalk

    Correct, my understanding is the 18" rule was changed to apply to T2 mode for a crushing distance.


    For normal operation your distance should be the stopping distance of the robot plus the mesh fence reach though distance.