    Hi everyone
    I'm a beginner at programming fanuc but getting closer and closer to a to a beginner + level:winking_face:
    We usually program specific zone (or space) between the robot and the PLC in ethernet IP.
    These Zone are NOT SAFETY relative, the robot basically tell the PLC he is inside a zone and the PLC should not move anything inside this zone until the robot is out.
    I read articles using DCS but you cannot use a DO there.
    I could use REF POS where you basically config how close from the point you can be using all Jaxis and set a proper DO, but REFPos use joint position and I want to define a box.
    I did want to use Space fnct but this are linked to Interference Space setup and you need DI input, priority, alarm check and so on...
    Is their an specific option to use? or I need to use LPos using a BackGround program where I calculate the distance between the TCP current position and a specific point and set a DO when the robot is getting close to that point.
    Thank you.
  • Haze
    15
    • June 6, 2025 at 11:58 AM
    • New
    Normally that is exactly what space function is for.
    Prepare a signal in your PLC, to enable access for the robot and use the robots DO to know when the space is blocked.
  • retobor
    17
    205
    • June 6, 2025 at 1:23 PM
    • New
    As an option, you can map your DCS safe signals to an NSI (Non Safe Input) which interconnects to standard I/O using Safe I/O mapping. So, you can in theory use D I/O.
  • MoEL
    102
    • June 6, 2025 at 1:29 PM
    • New
    Quote from ashley
    You can use SpaceFcnt without DI
  • Mikael
    5
    49
    • June 6, 2025 at 1:39 PM
    • New
    You can connect your DCS CPC zone to a DI. Just configure your DIs for Rack 36, slot 6.
    Then you use interconnect to control your DO to the PLC.
  • ashley
    58
    • June 6, 2025 at 2:09 PM
    • New
    Thank you everyone for your answer. Space func does the job indeed
    btw use : $RSPACE1[SPACE_NUM].$NO_USE_DI=TRUE to configure the SPACE_FUNC without the need of DI AND the need of alarm actif (you cannot let DI[0] if alarm disable , you will have a message from the teach that states you need to display an alarm if DI[0]
    best regards
    Images
      • 228.27 kB
      • 1,277 × 582
      • 9
    Edited 3 times, last by ashley (June 6, 2025 at 3:07 PM).
Similar Threads
  • Activating safety zone by input
    • ROB_ER
    • March 18, 2025 at 1:52 PM
    • KUKA Robot Forum
  • Discuss How to Start Safe Mode while moving. Ensuring Human Life Safety, Avoiding Collisions, Repairing After Collisions, Electrical Failures on KUKA KRC2ed05 Robot.
    • PhunxamLinda
    • December 20, 2024 at 12:18 AM
    • KUKA Robot Forum
  • abb safe zone
    • Jleon89
    • August 6, 2024 at 9:19 PM
    • ABB Robot Forum
  • Limiting speed of the robot
    • monspi
    • April 4, 2024 at 1:23 PM
    • KUKA Robot Forum
  • External Deadman via Robot I/O
    • Ace's_Robot_Delivery
    • February 19, 2024 at 4:43 PM
    • Fanuc Robot Forum
  • Safe Operation Cartesian protected spaces
    • jaiiyer
    • November 9, 2023 at 11:01 PM
    • KUKA Robot Forum
  • Safety zone Kawasaki ZX
    • Homework55
    • August 29, 2023 at 3:14 PM
    • Kawasaki Robot Forum
  • Robot Stops Before Violating a Safe Zone's Tool Position Supervision
    • gmumaugh
    • November 11, 2022 at 4:05 PM
    • ABB Robot Forum
  • SafeMove: Synchronization vs Safe Zones
    • SkyeFire
    • August 4, 2021 at 11:45 PM
    • ABB Robot Forum