Hello,
As the title says I'm trying to get my SCARA 12iA (R30iB compact plus) robot going using the JRM18 jumper connector.
I have recieved this new robot, registered it and the only thing that keeps me from testing is Operator panel E-stop alarm.
So far I soldered some pins I found in the Maintenance manual for R30iB Compact Plus namely:
24VEXT_IN (1pin) --- 24V-2 (2pin)
24V-2 (3) --- EES1(6) --- EAS1(7)
0VEXT (35) --- 0V (36)
0V (37) --- EES2 (40) --- EAS2 (41)
(6 cables total)
I connected the JRM18 jumper connector to the controller and started the robot, but the fault is still present, its the only fault that comes up. Is there anything I could do, maybe some settings in robot tech pendant need to be changed or is it possible that I may have blown a fuse before and I just got no alarm on TP ?
Any and all help would be much appreciated and in case you need more information please tell me.
-Bapps