  4. Kawasaki Robot Forum
Issue with Continuous Cycle in Kawasaki CP180L Palletizing System
  • Gus_akira
  • March 12, 2025 at 4:34 AM
  • Gus_akira
    16
    • March 13, 2025 at 12:32 PM
    • #21
    Quote from kwakisaki
    So it completes the pallet then?
    The robot only runs for one pallet; after that, it gets stuck in a loop.
  • kwakisaki
    694
    4,770
    • March 13, 2025 at 12:34 PM
    • #22
    ; Last Bag R C/V
      IF (SIG(1009)==TRUE) THEN; Last Bag R C/V
        SIGNAL (22); Job Complete R ==> Forced pallet exit
        bag_no_r = 0
        GOTO 10
      END
    ; Last Bag L C/V
      IF (SIG(1008)==TRUE) THEN; Last Bag L C/V
        SIGNAL (21); Job Complete L ==> Forced pallet exit
        bag_no_l = 0
        GOTO 10
      END
    SIGNAL (21) and SIGNAL (22) look like they need swapping.
    pg14 uses SIGNAL 21 for last bag right, but above you have SIGNAL (22)?
    Also recommended not to place SIGNAL outputs in parenthesis either:
    SIGNAL 21
    SIGNAL 22
  • kwakisaki
    694
    4,770
    • March 13, 2025 at 12:37 PM
    • #23
    You need to recheck your master for correct signals for left and right.
    Something appears mixed or swapped over between left and right selection , complete, reset.
  • kwakisaki
    694
    4,770
    • March 13, 2025 at 12:44 PM
    • #24
    The following areas of code need to checked to ensure left and right logic is applied for the correct sequencing:
    ;Last Bag Change Logic
    ; Last Bag R C/V
        bag_no_r = 0
        GOTO 10
      END
    ; Last Bag L C/V
        bag_no_l = 0
        GOTO 10
      END
      IF (SIG(22)==TRUE) THEN; Job complete R
        bag_no_r = 0
        GOTO 10
      END
      IF (SIG(21)==TRUE) THEN; Job completed L
        bag_no_l = 0
        GOTO 10
      END
    I think these are mixed up between left and right according to your sequence.
  • Gus_akira
    16
    • March 13, 2025 at 1:12 PM
    • #25
    THANK YOU VERY MUCH, IT'S SOLVED!
    The problem was that as the robot programmer and the PLC programmer, I didn't align the logic properly with the left and right conveyors.
  • kwakisaki
    694
    4,770
    • March 13, 2025 at 1:18 PM
    • #26
    Nice.......glad to hear you've resolved it............:top:
  • kwakisaki
    694
    4,770
    • March 13, 2025 at 1:29 PM
    • #27
    FYI..........
    Your initial coding was valid AS Language format for IF's and SIGNALS, but as mentioned I have seen instances where the return of the arguments comes back incorrectly plus it is quite easy for 'us' to misread or insert some typo's etc.
    Regarding the suggestions of changing your code referencing the IF's and the SIGNALs, it makes it clearer and easier to read and eliminates incorrect returns of arguments.
    So reviewing everything, it looks like it was the 'mix up' of the logic that was probably the issue.
    Keep that PAUSE command in your troubleshooting tool box, very effective command to use outside of the usual use of it.