Fanuc Ethernet/IP configuration over Karel
  • 22Actuators
  • March 5, 2025 at 3:38 PM
  • 22Actuators
    7
    Hello all!
    I'm trying to configure an ethernet IP scanner connection using KAREL only.
    I've manage to replicate the adapter settings using SET_VAR, but can't set up the scanner info, such as vendor, product code or Out assembly instance and in assembly instance.
    Does anyone have any clue?
  • Go to Best Answer
  • DylanNOEL
    25
    106
    • March 5, 2025 at 4:29 PM
    Look in SYSEIP.VA,
    this is my setup for ethernet/ip slot 2
    Please don't let me google it for you :winking_face:
  • 22Actuators
    7
    • March 5, 2025 at 4:47 PM
    Sorry,
    I forgot to add some further context.
    I've tried to Set_Var with both EIP_SC[1].$Vendor and $PX_Vendor, but it refuses to assign to them that way.
    I thought they were read only.
    it's the same for the rest of the variables in the EIP SC.
    Can I edit the .va directly?
  • pdl
    272
    1,549
    • March 5, 2025 at 10:34 PM
    Have you tried using KCL commands in your Karel program? They seem to work for me:
    PROGRAM KCL_TEST
    %ENVIRONMENT kclop
    VAR
    	status:	INTEGER
    BEGIN
    KCL ('SET VAR $EIP_SC[1].$VENDOR=123', status)
    END kcl_test
  • pdl
    272
    1,549
    • March 5, 2025 at 10:57 PM
    • Best Answer
    Just for a test, I tried using the conventional Karel Set_Var built-in procedure:
    PROGRAM KCL_TEST
    %ENVIRONMENT kclop
    VAR
        status:    INTEGER
        vendor_int: INTEGER
    BEGIN
        --SET_VAR Direct
        vendor_int = 789
        SET_VAR(1, '*system*', '$EIP_SC[1].$VENDOR', vendor_int, status)
    END kcl_test
    I had no issues changing the variables this way either. Could you post your code that is failing?
  • 22Actuators March 6, 2025 at 9:02 AM
    Selected a post as the best answer.
  • 22Actuators
    7
    • March 6, 2025 at 9:04 AM
    Quote from pdl
    PROGRAM KCL_TEST
    %ENVIRONMENT kclop
    VAR
        status:    INTEGER
        vendor_int: INTEGER
    BEGIN
        --SET_VAR Direct
        vendor_int = 789
    END kcl_test
    Thank you!
    As it turns out, when I was comparing my code with yours, it appears that I dropped a * after *system and never noticed.