    Hello guys, once again,
    I was wondering if any of you created a project where, the PLC is the Adapter and the robot is the Scanner. It's for a CRX-10iA/L and for Siemens PLC S7-1200. I'm using Ethernet/IP between them to communicate. I was wondering if making the PLC to be the Adapter and connect it to the 3rd port, if it could work properly and if so, where do I put the .eds files of my PLC in to the robot?
    Thank you for your time guys!
  • gpunkt
    138
    492
    • February 5, 2025 at 9:34 AM
    1. Don't use the 3d port (CD38C) for anything other than GigE-cameras, instead you'll have to do with the first two ports. ALSO IMPORTANT: Don't set the two ethernet interface's IP-addresses to the same subnet
    2. It's (still) not possible to load a .eds-file to a FANUC robot controller as far as I'm aware, you need to punch in the settings manually
  • warhound96
    44
    • February 5, 2025 at 9:38 AM
    gpunkt thank you for the info! I did put them manually after all, but still got nothing. As for the 3d port, I already left it and I'm using only 1 & 2 now, thank you for the info on that. Also, the subnets are different. At the end, it didn't work at all so I set to be scanner again and I'll see what else I can do then. Thank you again for your time!