hi
my profinet card cp1616 (6GK1 161-6AA00) on kuka krc2 ed05 firmware is 2.1 but i don't have gdsm of this firmware for tia portal
anyone has gdsm of cp1616 for tia portal?
hi
my profinet card cp1616 (6GK1 161-6AA00) on kuka krc2 ed05 firmware is 2.1 but i don't have gdsm of this firmware for tia portal
anyone has gdsm of cp1616 for tia portal?
Did you try CP1616 GSDML ?
I would try to use Step7 instead of TIA Portal to configure these old CP1616 card.
Did you try CP1616 GSDML ?
Yes but thats gsdml for newer version of firmware
I would try to use Step7 instead of TIA Portal to configure these old CP1616 card.
My all project created on tia portal v19
In theory, is possible to make this setup work just with TIA Portal.
In practice, I can't say so.
You will need two hardware configurations to make this work. One inside the PLC, another inside the CP1616 on robot controller.
You can use TIA to configure the PLC side of Your system but, again, my advice is use Step7 on robot side. In my personal experience, every time we tried make robot side with TIA, we went on trouble.
And, about the GSDML, I searched my stuff here, but didn't found this specific version.
In the post referenced by hermann, there is a file called GSDML-V2.0-Siemens-CP16xx-20070524 .txt. These files are not newer. They are pretty old.
Change the extension from .txt to .xml
File version is V2.0, but there are 2.1 modules inside.