Hello,
I am having issues with Group inputs over Ethernet IP. I have an LR Mate 200id robot with an R30IB Mate Plus controller, and a Omron PLC. I've set this up many times and it always works
When the PLC sends an integer the Group inputs do not populate but the Digital inputs do.
For example, If the PLC sends a 1 to GI 1, The Group input reads 0 but the Digital input associated With the GI is on
The I/O is configured as such
Thanks
Range | Rack | Slot | Start | Status | ||
DI [1-152] | 89 | 1 | 1 | ACTIVE | ||
DI [153-153] | 36 | 6 | 1 | ACTIVE | ||
DI [154-160] | 36 | 6 | 10 | ACTIVE | ||
DI [161-296] | 89 | 1 | 153 | ACTIVE | ||
GI | Rack | Slot | Start Pt | Num Pts | ||
1 | 89 | 1 | 169 | 16 | ||
2 | 89 | 1 | 185 | 16 |