SRVO-037 IMSTP
  • mcminn6
  • September 24, 2024 at 1:31 PM
  • mcminn6
    34
    Fanuc R-2000ib/210f Robot. R-30iA controller.
    Robot is controlled by a PLC through ethernet but keeps randomly stopping with a SRVO-037 IMSTP alarm. Some cycles it runs without issue, but others it will stop with this alarm. I am not a PLC programmer but I assume this alarm is triggered from the PLC? Any ideas on what could cause this would be appreciated.
    mortoch
    16
    202
    • September 24, 2024 at 1:43 PM
    If you can access PLC program you should be able to find the bit that is triggering the alarm and see what cause is.
    gpunkt
    127
    476
    • September 24, 2024 at 2:30 PM
    The IMSTP-signal is part of the remote interface and needs to be TRUE for the robot to be able to run.
    The reason you get the SRVO-037 alarm is because this signal dropped (turned to FALSE).
    Since this signal is coming from a PLC (through Ethernet), then you better find out why the PLC resets this signal.
  • mcminn6
    34
    • September 24, 2024 at 3:04 PM
    We are trying to find out but our plc programmer can't find the issue.
    He monitors the robot heartbeat and thinks that we are dropping the heartbeat which is sending the IMSTP alarm. The heartbeat is configured through an output for the plc to monitor. When I watch the teach pendant, every now and then the output does appear to get stuck on either off or on for an extra second or two. But I believe that is just a lag because the cell interface is working correctly.
    gpunkt
    127
    476
    • September 24, 2024 at 5:16 PM
    The visual representation of signals on the TP is not the same thing as the actual status of the physical signal (bus or hardwired). There's always the factor of lag in the display and so on.
    Don't know how your heartbeat function is set up, but it would be possible to build a simple heartbeat function using BG Logic.
    Also, to be clear, the PLC isn't sending an IMSTP alarm, the IMSTP signal drops (whether it's due to logic in the PLC, bad connection on the bus, or whatever), the robot recognizes this state and issues an alarm (SRVO-037) because of this state.
  • hermann
    407
    2,613
    • September 27, 2024 at 5:45 AM
    Easy test: change plc program that imstp is forced to high. If issue is gone, you have a problem with imstp and watchdog, otherwise you must search at a different place.
  • sborchshev
    39
    • September 30, 2024 at 9:54 PM
    How long is your Ethernet cable? is it shielded?
Users Viewing This Thread
  • 1 Guest