  3. Cobot Help and Discussion Center
  4. other Cobots
Techman/Omron cobot ProfiNet problems
  • PZUFIC
  • July 11, 2024 at 10:46 AM
  • PZUFIC
    I'm new here, hoping that someone has experience with Techman/Omron cobots.
    I'm trying to communicate with Siemens PLC over ProfiNet using TMFlow. I'm successful with reading the values, but unable to write anything.
    I'm trying like that: Set block -> Variables -> profinet_write_output_bit(518, 0) = 1.
    It runs fine, but it does nothing. I also tried doing it like so: result = profinet_write_output_bit(518, 0, 1) which should be more logical way according to TMscript manual, but it does not accept the input.
    After 9 years of PC and robot programming I'm really struggling with that dumb graphic way of doing it.
    We are arranging a Techman course in the future, but that's the only thing that I need to solve in order to make the application work.
    Thank you very much in advance.
    Best regards,
    Primož
  • 95devils July 11, 2024 at 11:01 AM
    Approved the thread.
  • joost
    • July 11, 2024 at 3:48 PM
    Hi primoz,
    I think you are writing in a part of the Profinet table that is already in use by the cobot itself, to expose the DO to profinet devices.
    You should write here:
    These registers are "free memory" for you to do what you want.
    Images are from the TMFlow 2.14 software manual, appendix F.
    Hope this helps!
  • PZUFIC
    • July 16, 2024 at 8:44 AM
    Hi Joost,
    it works, you were right.😀
    Thank you very much for your help.
    Best regards,
    Primož
  • Techman
  • Techman Robot