Start with a kuka Robot

  • wag_FFU
  • June 5, 2024 at 9:09 AM
  • Thread is Unresolved
  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 5, 2024 at 9:09 AM
    • #1

    Good Mornings.

    I´m currently working as PLC programmer / Robot configuration . We have accepted a job with a KUKA robot krc4 and I´m in charge to write the PLC program to manage the robot and also configure the robot automatic external. I ve a good experience with Fanuc and I ve used KUKA robot somethimes, but only to teach/change programs, never configured to work in Aut External with a PLC. The robot connection is the always good Profibus DP.

    The manual explain which signal are used and also the diagrams with the timing but I have some question about the signal mapping with DI/DO

    I ´ve used Orange edit and I´ve found than some signal are mapped in $Machine.dat and other are configured as variable in $Config.dat.

    The input and output address are configured from 1 to 1024, some in the first bits, other near 1024 ( 1025 always ON, 1026 always OFF). Can I change the input /output value to group them in the first 128 input/output number?

    Sound a dummy question but I can´t find this information, Thanks

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 5, 2024 at 1:02 PM
    • #2

    Yes you can... In fact you need to change them to be able to use EXT mode. You can use any free IOs although for EXT interface to work with your PLC, the Used IO range need to be whatever PLC can control. Normally one would use lowest IO so that user does not need to scroll much through HMI IO list. But .. there is nothing wrong with using IOs at the end of addressable space...such as 7800...7927 for example.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 5, 2024 at 2:21 PM
    • #3

    Thanks, I´ll change the input output mapping to match with my configuration.

    Another question, is kuka big endian or little endian? Have I to swap the byte if I send a 16 bit value to the Robot with a Siemens PLC? Thanks

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 5, 2024 at 2:31 PM
    • #4

    with Siemens you will need to swap bytes. normally this is done in WoV while mapping IO

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 5, 2024 at 2:34 PM
    • #5

    Thanks guys

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 5, 2024 at 3:36 PM
    • #6

    For someone with a Fanuc background, you can think of $IN and $OUT as DI and DO. System signals like $DRIVES_ON and $MOVE_ENABLE are equivalent of UOPs, and need to be mapped to specific $INs and $OUTs. However, KUKAs don't have the Local/Remote or SIO types options that Fanuc does. In this respect, KUKAs are much simpler.

    GI/GO equivalents are a bit odd relative to Fanuc. They're defined at the program level (using the SIGNAL declaration), rather than the system level,are declared by name instead of a number, and are "just" a group of DI/DO (any size between 2 and 32 bits) treated as a signed 32-bit integer. However, for multi-byte signals, any byte-swapping has to be handled in WorkVisual. One thing to watch out for is that any SIGNAL less than 32 bits will never trip the 32nd "sign" bit, and so will act like an unsigned SINT or DINT. Back when I/O tables were smaller, we did a fair number of programming tricks to get around this, but these days it's probably just simpler to declare everything as 32bit, even if that's a bit wasteful of byte space.

    KUKAs also have no system level equivalent of PNS/RSR/etc. Instead, everythind is done at the program level. To facilitate this, every KRC includes the CELL.SRC module, along with a series of global variables that can be confgured through WoV or through the pendant menu (Config->I/O->Auto-External), mostly with names that include "PGNO" in the variable name. You replace the "example" lines in the CELL program with calls to your own programs. Or, you can ignore CELL and write your own "main" program from scratch.

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 5, 2024 at 4:13 PM
    • #7

    OrangeEdit and other text editors are fine to manipulate programs but to configure KRC (this includes fieldbus configuration and IO mapping) you will have to use WorkVisual.

    It is a free app you can download from KUKA.

    next you will need to configure it:

    - KOP integration. KOP files are KUKA Option Packages. WorkVisual may use them when compiling or transferring project to robot. So you will need to get them from D:\ of the robot and integrate them into WorkVisual.

    - Any 3rd party devices will not be present in the DTM catalogs of WorkVisual. So you will need to import the device description files for each and every non-KUKA product into DTM catalog. than you may insert them from catalog into your project


    WorkVisual workflow:

    1. make backup(s) before touching anything

    2. do not create new project from scratch. this is possible but cumbersome and you need to have some insider knowledge. just do yourself a favour and the get working project from the robot, and apply your changes there.

    3. activate project by double-clicking on controller. this will allow you to see things differently (buis nodes can be expanded).

    4. if your project does not have X44 bus, add it

    5. add EK1100 (bus coupler) and any IO including profibus module(s) that you are palling to add. make sure type and order of modules is correct. usually PLC is master so robot would be slave and therefore need EL6731-0010

    6. name IOs unders Symbol editor

    7. map IOs, if needed do a byte swap

    8. when ready to transfer project to the robot, make sure no program is selected and you are logged in as Expert or higher.

    9. transfer project and activate it.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 5, 2024 at 4:15 PM
    • #8

    btw, it is possible to not have fixed IO mapping. for example one could remap the signals and do byte swap in Submit too. the advantage of this is that order or signals can be changed any time, even while robot is running. the disadvantage is that this needs program code that runs in Submit and therefore is slower and less practical for average user.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 5, 2024 at 4:22 PM
    • #9
    Quote from panic mode

    btw, it is possible to not have fixed IO mapping. for example one could remap the signals and do byte swap in Submit too.

    One working example of doing something like this can be found in the module P00, which is a support module for CELL and comes with every KRC. CELL's options include operations similar to PNS and RSR, along with adjustable size of the "word" for selecting programs, using negative numbers, and a few others I've never actually used. P00 is what steers through all those options and does different math on the PGNO values. It doesn't do byte-swapping, but there's a lot of other bit-manipulation it does that should provide some insight on what's possible and how to do it.

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 6, 2024 at 2:55 PM
    • #10

    I ´ve to download also workvisual to configure the Profibus/Profinet interface . I ´m current reading the kuka manual and if I ´ve understood correctly, the CELL program must be execute to enable the kuka robot to work in automatic extern mode. Have The operator have to execute it manually and then select the automatic extern mode?

    I can swap byte with the SPS, no problem

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 6, 2024 at 2:56 PM
    • #11

    "the CELL program must be execute"

    no...

    Cell program is what KUKA supplied to make use of EXT mode easier and consistent. but you CAN remove it and make your own implementation if you know what you are doing. CELL is used in particular when PLC need to be able to choose between several robot programs. if you only have ONE program, then this can be run directly, without CELL.

    "Have The operator have to execute it manually and then select the automatic extern mode?"

    sort of...

    The default is that operator selects the CELL, runs it in manual until BCO is complete, then change mode to EXT to let PLC take over.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 6, 2024 at 3:09 PM
    • #12
    Quote from wag_FFU

    I can swap byte with the SPS, no problem

    If you want to use CELL with a multi-byte PGNO, you don't want to rely on using the SPS for byte-swapping, due to the way CELL and P00 handle reading in the PGNO values (unless you want to start re-writing parts of P00). On modern KRCs, the best way to handle byte-swapping is through WorkVisual.

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 7, 2024 at 10:20 AM
    • #13

    Ok, I´ve installed all XML and GSD File than I need, the KUKA Manual are not clear about the file you need to configure it. I ´ve installed the Beckoff EK1100 xml, the EL6731 xml and also the EL6731-0010 GSD (I ´ve found an old Panic mode´s Thread with the File ).

    If I´ve understand right, I can configure the communication with the PLC with a defined number of byte/word , like a normal Profibus DP device, and then I have to assign these byte to $in and $ out in IO Mapping between KRC I/Os and fildbus.

    I can also split these bytes into bits or grouping in words and assign them to $IN or $OUT.

    So I´m planning to change my plan, and don´t change the signals address in $Machine.dat but simply mapping the $in/$out to the desired PLC In/Out number

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 7, 2024 at 2:38 PM
    • #14
    Quote from wag_FFU

    So I´m planning to change my plan, and don´t change the signals address in $Machine.dat but simply mapping the $in/$out to the desired PLC In/Out number

    Usually we edit both. The default addresses in $MACHINE.DAT are just there as placeholders, and tend to be a bit scattered around in the $IN/$OUT arrays. You could keep $MACHINE.DAT unchanged, and just do bit-by-bit addressing in WoV, but anyone who works on that robot in the future will curse your name.

    WoV address mapping is best handled in blocks (say, 1-1000 to the PLC, 2001-2100 to the EOAT, 2201-2300 to the fixture tooling, etc). Then you edit $MACHINE.DAT (or, really, don't directly edit that file, use the Configuration menu instead, let the system edit the files for you) to connect specific bits to specific $IN/$OUTs inside those blocks.

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 10, 2024 at 4:44 PM
    • #15

    Thanks, I´ve planned to use the first bytes to map the communications.

    Another questions, what about the calibration? Are the kuka Robots already calibrated or I have to execute some sort of "first calibration"?

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 10, 2024 at 5:23 PM
    • #16
    Quote from wag_FFU

    Another questions, what about the calibration? Are the kuka Robots already calibrated or I have to execute some sort of "first calibration"?

    KUKAbots are usually Mastered (have each axis zero'd) at the factory, although doing a Check Mastering is always good on first powerup. Mastering is done using a tool called the EMD, which plugs into the robot's electronics and touches off a special precision-machined target inside each axis. DO NOT USE THE PAINT MARKS -- those just indicate the start point for the EMD motion.

    Do this before mounting any tooling to the robot. Then, you have the option later of doing an updated Mastering with the load mounted (and Payload data entered), which will attempt to "tweak" the Mastering to account for any sag caused by gravity on the payload. Then there's some extra steps if your robot is an Absolute Accuracy or High Accuracy model, which have had extra calibration at the factory.

    Most of the time, a simple Mastering and entering correct payload data is all that's needed for a KUKA to be very precise and repeatable. The extra steps are usually only necessary for applications that rely on accuracy rather than precision (they are NOT the same thing).

    Quote from wag_FFU

    Thanks, I´ve planned to use the first bytes to map the communications.

    Note: as a general rule, avoid using the byte that contains $IN 1026 and 1025. I also usually avoid the matching $OUT byte, just for symmetry. For historical reasons, back when KRC1s had exactly 1024 I/O and no one thought we'd ever need more because the "best" on the market was usually 128, $IN 1025 was assigned as an "always True" bit, and 1026 as an "always False" bit. Then they couldn't change that when the KRC2s started shipping with 2048 I/O (without breaking backwards compatibility), so now everyone just avoids those bytes.

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,037
    • June 10, 2024 at 5:23 PM
    • #17

    KUKA robots come mastered from the factory. however if you do have access to EMD, it does not hurt, in fact it is a good idea to remaster it. if you do not have mastering tool, stay away from this.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 11, 2024 at 8:40 AM
    • #18

    Thanks for the story about kuka robot and in 1025, 1026, this things are always intersting, I worked only one time with a KRC1, the 4 line black and white display was horrible!

    No, I don´t have an EMD, in fact I should buy it, but the factory where the robot should be mounted use only kuka robot, they will have plenty of EMDs ( I hope...).

  • Online
    SkyeFire
    Reactions Received
    1,042
    Trophies
    12
    Posts
    9,388
    • June 11, 2024 at 5:41 PM
    • #19
    Quote from wag_FFU

    I worked only one time with a KRC1, the 4 line black and white display was horrible!

    ...the KRC1 had a color VGA (800x600), 256-color display. The only KRC that matches your description was the KRC32, with the triangular-key keyboard where each corner of each key was a different letter/number.

    Quote from wag_FFU

    No, I don´t have an EMD, in fact I should buy it, but the factory where the robot should be mounted use only kuka robot, they will have plenty of EMDs ( I hope...).

    They should. If they don't, you can do it by feel -- several forum threads talk about field-expedient mastering. It's an old trick for dealing with customers who don't have an EMD (or lost it, or broke it, or....)

  • wag_FFU
    Reactions Received
    4
    Trophies
    2
    Posts
    86
    • June 12, 2024 at 10:12 AM
    • #20

    yes, It was a strange and old teach pendant with the triangular shape buttons key, I worked on that robot only for 2 hours 10..12 years ago. The robot movement where terrible, klunky and with a lot of acceleration/deceleration between the points with no reason.

    One question about Home positions, I have the $in_home , $in_home_1... output only when the robot is that positions. Are declared as global positions, so I can use it and save it in any programs.

    Of course I can´t change the name of the position, but what about if I want to use different points name? Have I to create my global point and a routine to check the robot position and compare with these points? Or there is a list where I can write my point name and the robot will automatically compare with the current robot position? And yes, Fanuc has it.. but where are speaking about Kuka.

Advertising from our partners

IRBCAM
Robotics Channel
Robotics Training
Advertise in robotics
Advertise in Robotics
Advertise in Robotics

Job Postings

  • Anyware Robotics is hiring!

    yzhou377 February 23, 2025 at 4:54 AM
  • How to see your Job Posting (search or recruit) here in Robot-Forum.com

    Werner Hampel November 18, 2021 at 3:44 PM
Your browser does not support videos RoboDK Software for simulation and programming

Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000

Thread Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000

Similar Threads

  • Interrupt when testing in T1

    • Stampy
    • January 26, 2021 at 6:54 PM
    • KUKA Robot Forum
  • Editing Reference Tool in Inline Form point programmatically

    • snewk
    • March 29, 2024 at 8:10 PM
    • KUKA Robot Forum
  • Interrupt Example

    • SkyeFire
    • March 18, 2021 at 8:25 PM
    • Manuals, Software and Tools for KUKA Robots
  • Interrupt Not Triggering

    • Ahiers
    • June 20, 2023 at 10:24 PM
    • KUKA Robot Forum
  • KSS00455: Error while reading KrcExtConfgMsg.xlm > KRC_IO.xml

    • MHammer
    • March 13, 2023 at 12:36 PM
    • KUKA Robot Forum
  • INTERRUPT

    • Asimooo
    • January 2, 2023 at 11:02 AM
    • KUKA Robot Forum
  • program explanation

    • Abhi123
    • January 20, 2022 at 1:27 PM
    • KUKA Robot Forum
  • RSI distance control with ANIN problem.

    • PiotrEDC
    • July 22, 2021 at 6:06 PM
    • KUKA Robot Forum
  • ConveyorTech stop motion when receive a zero coordinate

    • ZorgCat
    • December 10, 2020 at 3:25 PM
    • KUKA Robot Forum
  • Continue program from jog position

    • Mathias Voegtle
    • October 10, 2020 at 8:28 AM
    • KUKA Robot Forum
  1. Privacy Policy
  2. Legal Notice
Powered by WoltLab Suite™
As a registered Member:
* You will see no Google advertising
* You can translate posts into your local language
* You can ask questions or help the community with your knowledge
* You can thank the authors for their help
* You can receive notifications of replies or new topics on request
* We do not sell your data - we promise

JOIN OUR GREAT ROBOTICS COMMUNITY.
Don’t have an account yet? Register yourself now and be a part of our community!
Register Yourself Lost Password
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on Google Play
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on the App Store
Download