Hardware I/O, CRX-25i
  • Rick petrous
  • May 22, 2024 at 11:29 AM
  • Rick petrous
    5
    I have CRX-25i with R-30, trying to triger Hardware digital output of the robot directly (Without PLC) . I configuered rack ,slot, and Start point according to 48 1 1, and mapped that to DO[81]. The wiring is also 24v and 0 v from card to sensor and getting the signal of DO[1] , but still no output signal.
    Is there any pre-wiring over the card ?
    Is there any pre configuration over the variables?
    I am newly experincing Fanuc, that would be perfect to have a general instruction about the first configuration of I/Os.
    Grazie
  • Go to Best Answer
  • 95devils May 22, 2024 at 11:38 AM
    Approved the thread.
  • gpunkt
    138
    492
    • May 22, 2024 at 1:36 PM
    You have probably made a mistake when wiring the supply +24VDC and/or the 0V.
    There are a few pins that needs to be connected. It's somewhat cryptic in the manual, but something like this:
    *24VDC must be supplied to DOSRC1 (pin 26)
    *0V-chain must not be broken, so daisy-chain all 0V (36-37-38-60-61-62-63)
    *If you want to use internal 24VDC, then jumper one of the 24V-2 (2, 3 or 4) to 24VEXT_IN (1), and also jumper from your 0V-chain to 0VEXT (35)
  • Rick petrous
    5
    • May 22, 2024 at 1:43 PM
    Thanks for your answer, This is a photo from my wiring.
  • gpunkt
    138
    492
    • May 22, 2024 at 2:26 PM
    That seems to be just the jumpers for the FENCE and EXT E-Stop circuits...
    You need to add also a chain for the 0V.
    Ask your local rep for the maintenance manual for the controller (R-30iB Mini Plus), there you will find which pin on JRM18 connector corresponds to which terminal on your break out board.
  • akay98
    13
    • May 23, 2024 at 6:11 PM
    • Best Answer
    Connect DOSRC 1 and DOSRC 2 to 24v
    Connect SDICOM 1 and SDICOM 2 to 0v
    After the connection your board will be powered up.
  • Rick petrous May 24, 2024 at 3:20 PM
    Selected a post as the best answer.