Fanuc robot jogging through DCS zone
  • zmac02
  • February 16, 2024 at 8:34 PM
  • zmac02
    Hi, has anyone ever seen a robot trip the DCS zone when the usermodel/robot comes in contact with the perimeter, but then when you engage the deadman to jog again, you can continue to jog right through the entire zone without tripping it again until you exit the zone and re-enter. It is a CPC with a cat 0 stop, and it shows unsafe when tripped but still can be jogged further into the zone. New robot and has RTCP function but I turned that off for now to troubleshoot this.
  • Nation February 16, 2024 at 8:42 PM
    Approved the thread.
  • DS186
    198
    1,049
    • February 16, 2024 at 11:38 PM
    Open the DCS Pos./Speed Check Setup Menu and set "Shift+Reset Direction Check" to ENABLE. If I remember correctly, it should then only be possible to jog the robot into the right direction (back into the safe zone).
  • Nation
    Typical Robot Error
    523
    1,903
    • February 18, 2024 at 12:37 AM
    This is probably not the case, but I was on a job where the previous integrator muted every zone the moment the robot was switched to T1 mode. Are the zones getting muted?
  • AlanL
    22
    77
    • February 19, 2024 at 1:40 PM
    Is there a disabling input in your DCS CPC?