How to get different status of robots by Karel Code
  • chibai
  • August 1, 2023 at 3:48 AM
  • chibai
    29
    I think most status are stored in some System Variables
    I guess there are several status as belowe:
    IsImergenceyStop?
    IsRobotInFault?(the Fault signal in TP)
    IsRobotEnabled?
    IsMoving?(the status of servo??)
    IsControllerReady?(the status of robot controller?)
  • dha
    29
    397
    • August 1, 2023 at 10:32 AM
    Instead of looking for variables, it is easier to link all UOP signals to Flags (if you don't use them for PLC communication) and read DO's in KAREL.
    - For E-Stop set DO in System > Config
    - For Fault read UO[6]
    - For enabled UO[1] and UO[2]
    - For robot motion you set DO in IO > Cell Outputs
    For reading DO use GET_PORT_VAL (2, port_nr, STATUS).
  • chibai
    29
    • August 1, 2023 at 12:45 PM
    Quote from dha
    Thank you for your reply, I also want to control the enable status of robot. But even if I set UO[2] as False, it will go back to True automatically.
    Is there any way I can change the status(enbaled/disabled) of robot?
  • dha
    29
    397
    • August 1, 2023 at 1:11 PM
    You need to toggle DO[] which is linked to UI[8: Enable].
  • SkyeFire
    1,060
    9,456
    • August 1, 2023 at 2:39 PM
    Quote from chibai
    UOs are system status outputs -- they are controlled by the operating system, not by your or your program.
    Likewise, the UIs are system inputs, and cannot be simulated. They must be linked to actual I/O signals.