Analog Output Voltage 0-10 V
  • robot-cnc
  • March 23, 2023 at 1:38 PM
  • robot-cnc
    432
    Hi !
    I am trying to transform a spindle speed RPM as an analog output from Kuka program to a Beckhoff Ethercat module EK1100-EL4004 ( 0-10V, 12 bit) to manage analogical command on spindle inverter, according with RPM speed inserted in program with a voltage between 0-10V. Kuka system is KSS 8.3.18.
    I have fallowing syntax, one, two three.jpg , I tried one with two combination but didn't work, spindle try to rotate but do not run properly. Then I read that $ANOUT[1]= cannot be a math formula, just -1 to 1, which means probably -100%...0%....100% scale, so $ANOUT[1]=1 maybe the correct synatx???
    Can you confirm me that?
    Or maybe there is another syntax variant:
    $ANOUT[1]=VOLTAGE, WHERE VOLTAGE IS CALCULATED AS IN spindle_on()
    $ANOUT[1]=1
    I would appreciate your help !
    Thank you
    Images
      • 170.13 kB
      • 931 × 739
      • 10
      • 268.29 kB
      • 708 × 824
      • 8
      • 271.84 kB
      • 708 × 824
      • 6
  • spiral
    146
    • March 23, 2023 at 1:45 PM
    Quote
    1 is equal to 10V.
  • DannyDJ
    67
    506
    • March 23, 2023 at 1:52 PM
    Hello, $ANOUT[1]=FACTOR*SET_RPMs formula should be OK, i have just programmed the same last week to set spindle speed from KRL program but on KRC2, but it should work also on KRC4.
    Did you measure with meter the actual voltage on EK1100-EL4004 on it's output, when you change the variable for the speed?
    So if you set maximum RPMs you should measure 10V and if you set max RMPs/2 you should get 5V etc...
  • panic mode
    1,297
    13,141
    • March 23, 2023 at 2:04 PM
    DECL REAL CONST MAX_RPMs = 3600.0 ; whatever the value may be
    DECL REAL SET_RPMs ; variable your program is to control
    $ANOUT[1]=SET_RPMs/MAX_RPMs
    SkyeFire
    1,061
    9,463
    • March 23, 2023 at 2:09 PM
    Quote from robot-cnc
    That is correct. The thing to keep in mind is that Analog hardware modules come in many varieties: 0V to 10V, -10V to +10V, 4 to 20mA, -5V to +5V, and others. Also, on the I/O side, they can come in 8-bit, 12-bit, 14-bit, and 16-bit binary ranges, not to mention they can be signed or unsigned.
    So ANOUT and ANIN can be seen as representing the signal range of the analog hardware module, from -100% to +100%. As such, ANOUT doesn't really know what voltage (or amperage) the module is actually producing (or receiving).
    So, sending ANOUT=1.0 to a 0-5V module would produce 5V, but setting ANOUT=-0.5 to a module with a -10V to +10V range would generate a -5V output at the physical layer. And so on.
  • robot-cnc
    432
    • March 23, 2023 at 2:56 PM
    Hi Skyfire,
    and what about first two opinions above?
    I cannot understand how worked for DannyDJ.
    The matter is RPM is variable, so allocation value 0%-100% should happen function of programmed RPM, therefore a math formula is a must, but PanicMode sugestion is contrary:
    $ANOUT[1]=SET_RPMs/MAX_RPMs or must add also
    $ANOUT[1]=1, meaning both code lines ?
  • robot-cnc
    432
    • March 23, 2023 at 3:01 PM
    Quote from DannyDJ
    yes, and is zero V.
    Beckhoff EL4004 is new and is ok.
    This is why I thought is a matter of syntax program that do not match and not sending to EL4004, right voltage in range 0-10V.
  • DannyDJ
    67
    506
    • March 23, 2023 at 3:10 PM
    Hi Skyfire,
    $ANOUT[1]=SET_RPMs/MAX_RPM and $ANOUT[1]=FACTOR*SET_RPMs gives you the same result
    in your FACTOR calculation you must divide with 1 not with 10 because $ANOUT[1] is max 1.0 not 10.0
    FACTOR=1.0/MaxRPM
    so $ANOUT[1]=(1/MaxRPM)*SET_RPMs = SET_RPMs/MAX_RPM
  • DannyDJ
    67
    506
    • March 23, 2023 at 3:39 PM
    yes, and is zero V.
    By zero V you mean it is 0 all the time regardless if you change the analog output values?
  • robot-cnc
    432
    • March 23, 2023 at 4:53 PM
    Thank you all !
    Variant that works is one from attached photo.
    Is fine, speed spindle got it from program.