KAREL Processing and IO desynchronization
  • Hello,
    This is my first post here but this forum has already been very helpful to me over the past few months. Thank you !
    There is my problem :
    We have a R-30iB mate plus who commuicate with PLC through Ethercat (Rack 106,Slot 1).
    Datas are processed with a KAREL program that is running with a RUN_TASK instruction and a "While true" with a Delay of 10 ms.
    Overall everything works fine except sometimes, where it seems that there is a gap between KAREL variables and GI. So i wrote a test code to confirm it:
    TestIO = GIN[10]
    IF TestIO <> GIN[10] THEN
        DOUT[145] = TRUE
        GOUT[11] = TestIO
        GOUT[12] = GIN[10]
    ENDIF
    GIN[10] is a variable from the PLC that increment from 0 to 255.
    I expected that TestIO <> GIN[10] would never be true and that DOUT[145] to be always FALSE, but it turns out that, totally randomly, DOUT[145] goes TRUE.
    The program can Run 10 minutes without setting DOUT[145] to TRUE, but can also sometimes goes TRUE 3 times in less than 1 minute. In the end, it always ends up going true at some point. I Can't hunderstand why.
    Does this sound normal to you and if so how do you explain it ? maybe there is a link with ethercat communication ?
    Thank You.
    Edited once, last by Kelidor ().
  • Place your Ad here!
  • 95devils
    Approved the thread.
  • Your inputs can change while the program is running. There is only 1 line if code between your assignment and conditional so it is pretty rare that it happens. This sounds like normal asynchronous IO behavior.
  • Ok I understood, thanks for your reply.
    I don't know why, but in my mind, the value of an IO would remain the same from the start of a task scan until the end of that same scan.
    PLCs operate in that way. The relationship between program line execution and I/O refresh is fixed. Robots generally cannot work that way, because the dominant factor in most robot program execution is motion. The robot controller must update its servo controllers, I/O driver, and other system resources on a fixed refresh cycle, every x milliseconds. But when the robot is moving from Point A to Point B, the time it takes to make that move might be one refresh cycle, or hundreds of them, depending on how far apart A and B are, and how fast the robot is moving.
    As such, in robots, the "background" refresh cycle is completely decoupled from the execution of program lines. A command to read Inputs or set Outputs might be instantaneous, but motion commands can be infinitely variable in execution time. And robot programs mix these "fixed-time" commands with "variable-time" commands. Line-by-line execution of a robot program follows the same set of rules, regardless of whether the program contains variable-time commands or not.
    The way this usually works is this: every refresh cycle, each subsystem in the robot gets a fixed "slice" of that time. The I/O update gets a fixed amount of time, the motion subsystem update gets a fixed amount of time, and the execution of the robot program gets a fixed amount of time. Ditto for multiple threads, background logic, etc. The total time is always a fixed value. While one subsystem is being "refreshed", all the other subsystems are "paused", in effect.
    So, even while running a very "tight" loop robot program, it is entirely possible --in fact, inevitable-- that eventually, an I/O refresh cycle will be called when the robot program is in beween two lines.
  • Quote
    All programs share the CPU time.
    The programs can and are interrupted in between. At which point this happens in the program cannot be predicted.
    Quote
    ((Why is this a problem?))
    At the time you read the input, it had a certain value. And this value is correct at this time.
    If you have to keep the value "synchronous" with the PLC, you have to program a handshake.
  • Thank you for this very detailed explanation.
    I now hunderstand better how Robots work.
    Quote
    PLC send a bit stream to the robot with a start command and data for motions instructions simultaneously.
    There is the way it works now.
    PLC : Cmd bit + Motion data stream -> to Robot
    ROBOT: Processing data Ok -> to PLC
    PLC : New Cmd bit + New Motion data stream -> to Robot
    ROBOT: New Processing data Ok -> to PLC
    etc...
    We use this exact same data stream and operation on other robot brand and that works well.
    The problem is, sometimes with Fanuc Robot , the start command signal is processed before some datas that have values of the bit stream n-1, resulting in wrong motion intruction.
    As you explained to me, probably because of some IO refresh cycle interruption.
    So For this Fanuc robot, I now have to find a way to ensure that all data stream is refreshed before sending the start cmd:
    @PnsStarter As you mentionned, the easiest way would be to add an handshake :
    PLC : Motion data stream -> to Robot
    PLC: Cmd bit -> to Robot
    ROBOT: Cmd bit Ok -> to PLC
    PLC : New Cmd data stream -> to Robot
    PLC: New Cmd bit -> to Robot
    ROBOT: New Cmd bit Ok -> to PLC
    etc...
    Almost all fanuc controllers run karel tasks at 8 ms internally. 10 ms is not an integer multiple of 8. This can lead to some unexpected scheduling of your task.