Select program automatically on startup in AUT mode
  • I added CWRITE in sps, but the program does not select on startup. Can anyone help? Thanks
    &ACCESS RVO
    &COMMENT PLC on control
    DEF SPS ( )
    ;FOLD DECLARATIONS
    ;FOLD BASISTECH DECL
    ;Automatik extern
    DECL STATE_T STAT
    DECL MODUS_T MODE
    ;ENDFOLD (BASISTECH DECL)
    ;FOLD USER DECL
    ; Please insert user defined declarations
    ;ENDFOLD (USER DECL)
    ;ENDFOLD (DECLARATIONS)
    ;FOLD INI
    ;FOLD AUTOEXT INIT
    INTERRUPT DECL 91 WHEN $PRO_STATE1==#P_FREE DO RESET_OUT ()
    INTERRUPT ON 91
    INTERRUPT DECL 92 WHEN $PRO_MOVE==TRUE DO RESET_LINESEL()
    INTERRUPT ON 92
    $LOOP_MSG[]=" "
    MODE=#SYNC
    $H_POS=$H_POS
    ;Automatik extern
    IF $MODE_OP==#EX THEN
    CWRITE($CMD,STAT,MODE,"RUN /R1/CELL()")
    ENDIF
    CWRITE($CMD,STAT,MODE,"RUN /R1/Program/t()")
    LOOP
    WAIT FOR NOT($POWER_FAIL)
    ENDLOOP
    ;FOLD
    END
    ;ENDFOLD
    DEF RESET_OUT ( )
    INT N
    MsgLoop(" ")
    IF REFLECT_PROG_NR == 1 THEN
    FOR N = 0 TO PGNO_LENGTH - 1
    $OUT[PGNO_FBIT_REFL + N] = FALSE
    ENDFOR
    ENDIF
    IF (PGNO_REQ>0) THEN
    $OUT[PGNO_REQ]=FALSE
    ELSE
    IF (PGNO_REQ<0) THEN
    $OUT[-PGNO_REQ]=TRUE
    ENDIF
    ENDIF
    END
    DEF RESET_LINESEL()
    $LINE_SEL_OK=FALSE
    END
    ;FOLD USER SUBROUTINE
    ; Integrate your user defined subroutines
    ;ENDFOLD (USER SUBROUTINE)
    ;ENDFOLD
  • kwakisaki
    Approved the thread.
  • ;Automatik extern
    ENDIF
    Unconditional CWRITE is a bad idea. You should have the second CWRITE inside an IF $MODE_OP==#AUT statement, like the #EX one above it.
    Is there another program selected before the robot is rebooted? And is it still selected after reboot is complete? Or is $PRO_STATE1==#P_FREE? I've never liked use CWRITE RUN without checking $PRO_STATE first and using CWRITE CANCEL beforehand.
    For example, this is from the Loop section of an SPS, designed to always Select CELL.SRC whenever the mode was changed to #EX, but the concept is the same:
                IF ($PRO_STATE1==#P_FREE) OR ($MODE_OP<>#EX) THEN
                   $FLAG[iProgramStarted]=FALSE
                ENDIF
                IF ($PRO_STATE1<>#P_FREE) AND ($MODE_OP==#EX) AND (NOT ($FLAG[iProgramStarted])) THEN
                   CWRITE($CMD, STAT, MODE, "CANCEL")
                ENDIF
                IF ($PRO_STATE1==#P_FREE) AND ($MODE_OP==#EX) THEN
                   $FLAG[iProgramStarted]=TRUE
                ENDIF
    Since you're trying to run the CWRITE in the Init of the SPS, you could do away with the $FLAG, which was used to ensure the CWRITEs were one-shotted, not cyclical. But you can see that the Interpreter is Cancelled first, then the CWRITE RUN is only executed after $PRO_STATE1 is #P_FREE.
  • Thank you for your reply. I test the program in KUKA Office Lite 8.63, is this effect?
    As I checked $PRO_STATE1==#P_FREE,and R on the top of the screen is grey. I change the code as the following, but still takes no effect. flag[3] is twinkle,0.5s true,0.5s fales.