    Hi I have a GP-25 YRC1000 Robot and I am trying to set up a way for the PLC to know that the robot is in certain Cube/Axis Interference zones.
    I currently have it setup in a concurrent job like so
    NOP
    *LOOP
    DIN B058 SOUT#(58) // CUBE/AXIS INTR2
    DIN B059 SOUT#(59) //CUBE/AXIS INTR3
    DOUT OT#(153) B058 //PURGE_ZONE
    DOUT OT#(154) B059 //NEST_ZONE
    Jump *Loop
    END
    Is this the proper way of doing it so that the PLC can see where the robot is or is there a better way.
    I tried through ladder editor but it was giving me an error when trying to output to #30243 external output
    Thank you
  • TSGIR
    81
    715
    • February 14, 2023 at 7:56 AM
    Hi
    Yes use concurrent job is one of methods for this work.
    Other method is use ladder editor, if you give error that is because the output address used in a BMOV instruction. For solve this problem check same as bellow:
    STR #70017
    BMOV #10010,510,#30030
    If you see the address #30243 is in this instruction. You must take out from it and use one by one.
    If you don't have knowledge to edit ladder don't use this method.
  • Jeffrocks99
    7
    • February 14, 2023 at 2:17 PM
    Thank you!