Program ABORTED in Auto mode

  • Hi

    we are facing strange problem in Fanuc Arcmate 100ic R30iB controller.

    When we are running the program in AUTO mode and pressing the emergency button then robot get stop and after reseting the emergency it is not starting from that program line and getiing aborted and go to start point.


    Regards


    Rupy

  • Verify the UOP Auto Assignment setup in the System Configuration.

    If it is set to "Simple", the fault reset signal is merged with the program abort.

    FAULT RESET and CSTOPI signals are separate in the "Full" assignment mode.

    Be aware though, that switching to "Full" remaps the UOP signals, which must be reflected in wiring and/or network UOP signals.

  • HI

    I checked the UOP auto assignment in configuration menu

    It is selected NONE.

    Still the same problem is occuring.

    Whenever we are pressing reset program is getting abort


    Regards


    Rupy

  • We are not using any PLC and Just a user panel is used for starting the program.

    I guess that user panel is connected to the robot controller via discrete wiring?

    I checked the UOP auto assignment in configuration menu

    It is selected NONE.

    Still the same problem is occuring.

    Whenever we are pressing reset program is getting abort

    Also check the UOP mapping under MENU > I/O > UOP > Config.