Prio-063 Bad I/O asg: Rack 0 Slot 1 (&2 & 3)

  • Hi,


    I've found multiple posts about this message, however it still is not perfectly clear to me.



    I keep getting the message:

    PRIO-063 Bad I/O asg: rack 0 slot 1

    PRIO-063 Bad I/O asg: rack 0 slot 2

    PRIO-063 Bad I/O asg: rack 0 slot 3


    The robot communicates with a PLC (PLC is master) via PROFINET. Controller is: R-30iB.


    In my summary file i found:


    DIN 1 - 256 RACK: 102 SLOT: 1 PORT: 1

    DIN 257 - 384 RACK: 101 SLOT: 1 PORT: 1


    DOUT 1 - 256 RACK: 102 SLOT: 1 PORT: 1

    DOUT 257 - 384 RACK: 101 SLOT: 1 PORT: 1



    According to this post (Settings to make Fanuc programming easier (From all of us)

    101 Dual Channel Profinet I/O Controller V9

    102 Dual Channel Profinet I/O Device V9


    However, as far as I know, we don't use dual channel Profinet?


    Could somebody suggest what I need to do, to prevent/solve these messages?


    Thanks in advance,


    Jarno

  • According to the data from your summary file you are using Molex Dual Channel PROFINET. You can also check this via MENU > STATUS > Version ID > ORDER FI.


    Could you please post a photo of your IO config screens. In your IO config you can clear the assignments with rack 0, slot 1, 2 and 3. After that, restart your controller and it should be fine.

  • My guess is this robot was created in Roboguide.

    It creates some default I/O, particuarly the Analog I/O



    So, write down the config of your DI/DO that is valid, then go MENU, I/O, select I/O device.

    F5 is CLR_ASG (clear asingment). Press F5, answer Yes, and then cyle power. it will get rid of your bogus asignments.

    I find it easier than manually looking for all the stuff thats bogus.

    Then enter your good configurations

  • According to the data from your summary file you are using Molex Dual Channel PROFINET. You can also check this via MENU > STATUS > Version ID > ORDER FI.


    Could you please post a photo of your IO config screens. In your IO config you can clear the assignments with rack 0, slot 1, 2 and 3. After that, restart your controller and it should be fine.


    I indeed do have the Dual Chan. Profinet option.



    I cannot select I/O device? This is digital in.

  • Thanks for your reply,


    I don't have I/O Device but I do have : "Link Device", I think this is the one, because I have the option for: CLR_ASG.


    What exactly happends when I execute this command? Do I have to configure my I/O again?