Analog Input Wiring
  • jariuscs
  • October 5, 2022 at 12:42 AM
  • jariuscs
    173
    Hello all
    working with an R30IA Controller.
    I got a AAD04B Analog input module and I would like to connect a Balluff Distance Sensor to it. I am new to analog signals and am confused how to connect the sensor to the input module.
    attached is a picture of the Fanuc module schematic and a picture of the Balluff sensor schematic.
    Any Help is much appreciated. thanks.
  • Go to Best Answer
  • pdl
    269
    1,531
    • October 5, 2022 at 1:30 AM
    What is the specific sensor model?
  • jariuscs
    173
    • October 5, 2022 at 5:19 PM
    Sorry I forgot to mention its a 4-20ma sensor
    the model is: BAW M12MF-ICC70G-BP02
  • DaveP
    23
    201
    • October 5, 2022 at 6:14 PM
    My guess is that you connect BN to +24VDC, BU to 0VDC and V2- on the analog input card, WH to I2+ AND V2+ on the analog input card, then install a 250 ohm resistor between I2+ and V2- on the analog input card. You can connect the sensor to any of the 4 channels, replace the 2 with the desired channel number (0-3).
  • jariuscs
    173
    • October 5, 2022 at 9:45 PM
    Thanks DaveP for the help.
    I wired it up like you described, except I used a 220 ohm resistor since that's what I had on hand. but now when I watch the readings on the teach pendant, I get about 2428 at the furthest distance, and it counts down to 0 after moving closer by only about 1/4 of the distance, and then it jumps up to 4096 and starts counting down again as I move closer ending at 1645 as the closest reading.
    so something is still off. Any ideas?
  • hermann
    407
    2,612
    • October 6, 2022 at 8:09 AM
    You don't need an external resistor. There are builtin resistors.
    Use the lower part of the schematic. So the rest of DaveP's suggestion should be OK.
  • jariuscs
    173
    • October 6, 2022 at 4:10 PM
    So when I wire it up like DaveP said, buy without the resistor, the count on the teach pendant starts at 1749 and then counts down to zero 3 times(and restarts at 4096), and then ends at 3538.
    nothing changes when I connect V2- and COM2.
    the power supply has no ground on the 24v side, so I don't have it connected to the FG2.
    I know the sensor works because I had it connected to a siemens 4-20ma input module and it worked flawlessly.
    Below is the schematic with the notes underneath visible, maybe that will tell you what I am missing.
  • HawkME
    568
    3,268
    • October 6, 2022 at 8:00 PM
    With analog signals it usually works best if all of your commons are tied to the same reference point, ground.
    That would mean connecting your DC negative to ground.
  • jariuscs
    173
    • October 6, 2022 at 9:24 PM
    Thanks HawkMe for the reply.
    I added a wire from 0v on the 24v side of the power supply to the Cabinet Ground, and also a wire from there to COM2, and it still act the exact same way. is it possible something is configured wrong? all 4 analog channels show up in analog inputs.
  • jariuscs
    173
    • October 6, 2022 at 10:19 PM
    also I did a test where I measure the voltage between V2- and I2+ and it starts at 4.4v and ends at 1.1v as I move the sensor closer, and it appears to move perfectly linearly. also I did an amp reading and it started at 0.005amps and ended at .018amps with my volt meter, which is 5-18ma with a proper milliamp reader it would probably come out a little better. I also tried the channel 3 instead of channel 2 and it reacts the exact same way. so what could I be missing? configurations maybe?
  • HawkME
    568
    3,268
    • October 6, 2022 at 11:25 PM
    • #11
    Can you show your config screen?
  • jariuscs
    173
    • October 6, 2022 at 11:46 PM
    • #12
  • jariuscs
    173
    • October 6, 2022 at 11:48 PM
    • #13
  • jariuscs
    173
    • October 7, 2022 at 12:30 AM
    • #14
    So I connected a little analog signal generator(model SG-002), and it acts the exact same way when I have it setup as 4-20ma, but when I change it to 0-10v and wire it accordingly, it also counts up and restarts the count at 0, but with voltage it counts up and resets 7 times, as opposed to 3 times with 4-20ma. maybe this can help narrow down the problem.
  • HawkME
    568
    3,268
    • October 7, 2022 at 2:39 AM
    • #15
    Can you give us a sketch showing exactly how you have it wired?
    *Edit*
    I see the wiring in the picture. Looks like it should work. I have 2 ideas to try.
    1. Ground FG3.
    2. Take a backup first incase you need to restore the IO configs. Then try setting the system variable $IO_AUTO_CFG to true. Then cycle power and see if it automatically creates the same config for your analog card (same rack slot/slot assignment).
    If that doesn't help then it may be time to call Fanuc.
  • jariuscs
    173
    • October 7, 2022 at 4:27 PM
    • #16
    Below is how I wired it. I even added the FG2 to ground.(except its wired to input 3 not 2 at the moment) adding FG to ground doesn't seem to make a difference though. when I look at the variable you mention I see it is already set to true. which is odd, because I thought I had configured all the IO myself.
  • HawkME
    568
    3,268
    • October 7, 2022 at 5:19 PM
    • #17
    Have you tried doing voltage instead of current? Disconnect I+.
    Maybe the analog card is bad. Do you have another one you could try?
  • jariuscs
    173
    • October 7, 2022 at 5:29 PM
    • #18
    I did try voltage with a signal generator, wired like you said, and the results were very similar to what I am seeing now, it counted up and reset to zero about 7 times instead of 3 times with current.
    Unfortunately I don't have another card to try, I bought this one brand new on eBay.
    this is the 16 bit version of the card, does this affect anything maybe? I might not need the high resolution, what I am after is a higher refresh rate then, when I had it run through a siemens PLC into the robot using group inputs.
  • HawkME
    568
    3,268
    • October 7, 2022 at 6:34 PM
    • #19
    Unless anyone else on the forum has a different idea, my guess is it is a bad card from Ebay. You could also call Fanuc to have them help troubleshoot. Can you buy a new card direct from Fanuc instead?
  • hermann
    407
    2,612
    • October 8, 2022 at 7:21 AM
    • #20
    Did you try another input, not always no 3?
Similar Threads
  • I/O Communication problem wiith PLC
    • Dalin
    • September 27, 2018 at 9:23 PM
    • Kawasaki Robot Forum
  • 24v analog outputs FANUC R-J3
    • Mark Krohn
    • March 24, 2020 at 12:12 PM
    • Fanuc Robot Forum
Users Viewing This Thread
  • 1 Guest