SRVO-218 Ext.E-stop/Servo Disconnect is the Error code that we are getting and we are trying to fix/bypass it the only thing I can find is (EES1-EES11, EAS1-EAS11, SD4-SD41,EES2-EES21) from looking in the manul but with looking inside of the box I am not seeing these wires, they might be misnamed very old robot. Thanks
Fanuc R-30iA Mate (Paint-Mate) SRVO-218
-
LucasYates -
September 29, 2022 at 2:05 PM -
Thread is marked as Resolved.
-
-
There is a sticker on the inside of the door that shows the terminals that the signals are on. If you are not using them then there will be little white plastic jumper plugs in them.
-
Will check that out, Thanks
-
Yup The sticker was under the fan and it was a orange thermal block that had EES1-EES11 EES2-EES21. I think it said Btop7 and there was a Btop6 under it. But Btop7 was right and just had to put 2 jumpers in it. Thanks again