unable to set DOs
  • zahid990170
  • July 27, 2022 at 6:24 PM
  • zahid990170
    41
    I am using SNPX option (HMI communication) with fanuc. The settings on the system variables are as follows:
    $SNPX_PARAM. $MODBUS_ADR = 1
    $SNPX_PARAM.$NUM_MODBUS = 2 (someone on the forum pointed out ,that this value should be above '0')
    Using SNPX_ASG parameter, I tried to map 15 digital outputs, DO[5] - DO[20] and 20 data registers, R[1] - R[20].
    For data registers,
    $SNPX_ASG.$ADDRESS = 51
    $SNPX_ASG.$SIZE = 40
    $SNPX_ASG.$VAR_NAME = R[1]
    $SNPX_ASG.$MULTIPLY = 1000
    For digital outputs,
    $SNPX_ASG.$ADDRESS = 91
    $SNPX_ASG.$SIZE = 15
    $SNPX_ASG.$VAR_NAME = DO[5]
    I am using pymodbus to read/write the above. I can write to data registers, using the following:
    client.write_registers(start_address, payload, skip_encode=True, unit=1)
    I use the following to write a DO.
    coil_response = client.write_coil(address=93, value=True, unit=1)
    But, on TP screen, when I MENU -> I/O -> Digital
    DOs are always appearing OFF on TP.
    When I read the status for the DO that was just written,
    coil_response = client.read_coils(address=93, count=1, unit=DEVICE_ID)
    it shows me that it has been 'set'
    Why can't I see the changed status of DOs on TP, or are they really changed.
    thanks,
    Zahid
  • EnergyAddict
    45
    133
    • July 27, 2022 at 8:17 PM
    I don't use SNPX, but did you properly configure the Digital Outputs robot side? Rack/Slot Numbers properly setup?
  • HawkME
    570
    3,270
    • July 28, 2022 at 2:59 AM
    Shouldn't you be writing to DIs, not DOs? The robot should be the only thing that can turn on a DO not an external source.
  • Erik Olsen
    62
    5
    196
    • July 28, 2022 at 7:27 PM
    Quote from HawkME
    I think HawkME is correct here. The status of your robot DO's arent changing on the teach pendant because they probably aren't changing at all. I'm not 100% sure that something like SNPX or PCDK cant change robot outputs externally but I wouldn't be surprised if they couldn't.
    If you wanted, you could map to some robot DI's and then use the IO-> INTERCONNECT feature on the robot to map those DI's directly to some Digital Outputs. A little bit of extra work on the robot side but this should pass your HMI signals through.
  • zahid990170
    41
    • July 29, 2022 at 11:35 AM
    thanks all for inputs. I read at a link
    Modbus with pymodbus - HackMD
    # Modbus with pymodbus Hence I can not understand well the usage from the [official document](http
    hackmd.io
    For 'single bit' you have DI, and DOs.
    And, when using modbus, DIs are 'read_only' whereas DOs are the ones that can be 'read and write'. Similarly, input registers are 'read_only' and holding registers can be 'read and write'.
    It was the reason to write to DOs using pymodbus library function.
    Further, modbus addresses in FANUC are one based, but in the library that we use pymodbus they are zero based.
    I noticed though, while
    $SNPX_ASG.$VAR_NAME = DO[5] (start point is DO[5], at address 90)
    I found out that in fact when I issued the following
    DEVICE_ID = 1
    ADDRESS_START = 90 # actual corresponds to DO[91] on Roboguide
    coil_response = client.write_coil(address=ADDRESS_START, value=True, unit=DEVICE_ID)
    I was able to TURN ON DO[91]. It should have been DO[5]?
    For current purpose, that is ok because I can use DO[91].
    thanks,
    Zahid
    Edited 2 times, last by zahid990170 (July 29, 2022 at 12:05 PM).
  • SNPX
  • modbus tcp/ip
  • pymodbus