    Hi guys!
    I am configuring a digital and analog IO board on an ABB S4 robot for welding control.
    I placed the card in Slot 1 of the case and installed the operating system. I selected the option during the installation of COMBI I/O.
    When initializing the board, there were no failures, but when forcing the analog output to some value, voltage levels are not generated on the board.
    I verified that the voltage levels coming from the internal source are being generated on the internal card, but when I measure the output nothing is generated.
    S4 Controller
    IRB1400 Arc
    IRBP 250R
    Miller Axcess 450
  • Lemster68
    301
    2,485
    Blog Articles
    7
    • June 14, 2022 at 7:36 PM
    Do you have the 24v IO power wired into the board? Do you get voltage on any of the outputs?
  • Skooter
    172
    2,058
    • June 16, 2022 at 4:06 AM
    There should be a ribbon cable going from the DSQC315 to XT10 terminal board at the back of the controller.
    XT10 is the analog portion of the DSQC315 Combi Board.
    Post a picture of the XT10 terminal connections so we can see if you're using the internal or external voltages.
    The DSQC315 and older DSQC224 use a split ribbon cable going to both XT10 (analog) & XT11 (digital) terminals. Part # 3HAB2128-1
    If you removed a DSQC223 Digital Board from slot 1, then you may only have the XT11 connections.
  • RobBrain34
    29
    • June 16, 2022 at 9:32 PM
    Problem Solved!
    There's a jumper inside the panel.