FANUC SOFT LIMIT TO AXIS DEGREES USING BG LOGIC
  • shriraj lonkar
  • May 4, 2022 at 8:01 PM
  • shriraj lonkar
    54
    How I can give a soft limit to the for the specific axis using bg logic
  • Go to Best Answer
  • dudz
    65
    • May 4, 2022 at 8:12 PM
    you can use $PARAM_GROUP[1].$LOWERLIMS[x] and $PARAM_GROUP[1].$UPPERLIMS[x] x=axis.
  • pdl
    269
    1,533
    • May 4, 2022 at 9:48 PM
    What are you trying to do. Those variables look to be correct, but they require a power cycle.
    DCS can dynamically limit an axis, but would require a safety input to enable and disable.
  • dudz
    65
    • May 5, 2022 at 12:39 PM
    Quote from pdl
    Oh, i didn't know about that. :frowning_face:
  • pdl
    269
    1,533
    • May 5, 2022 at 12:53 PM
    I should add, you could also use a JPC (Joint Position Check) to enable or disable another JPC.
    This is all covered in the DCS manual.
    Sergei Troizky
    70
    658
    • May 5, 2022 at 8:30 PM
    Quote from shriraj lonkar
    Is this to stop the robot if in forbidden area?
    If yes, this can be even done in BG logic, but the reaction time may appear insufficient for fast moves.
    Or, probably, may be done by Inteference Check, with fixture models modified programatically on demand.
    If, however, the axis limits are intended for MROT motion, they must be system settings and yes, require power cycle after modification.
  • shriraj lonkar
    54
    • May 7, 2022 at 12:47 PM
    Quote from pdl
    What are you trying to do? Those variables look to be correct, but they require a power cycle.
    DCS can dynamically limit an axis but would require a safety input to enable and disable.
    I WANT TO AVOID COLLISIONS DURING MANUAL JOGGING TO PREVENT GRIPPER FROM DAMAGE
    Images
      • 93.89 kB
      • 1,024 × 768
      • 17
      • 97.18 kB
      • 768 × 1,024
      • 15
  • shriraj lonkar
    54
    • May 7, 2022 at 12:49 PM
    Quote from Sergei Troizky
    Is this to stop the robot if in a forbidden area?
    Or, probably, maybe done by Interference Check, with fixture models modified programmatically on demand.
    If, however, the axis limits are intended for MROT motion, they must be system settings and yes, require a power cycle after modification.
    NO
    I WANT TO AVOID COLLISIONS ONLY DURING THE MANUAL JOGGING TO PREVENT THE GRIPPER FROM DAMAGE
    Images
      • 93.89 kB
      • 1,024 × 768
      • 10
      • 97.18 kB
      • 768 × 1,024
      • 8
  • Erik Olsen
    54
    5
    177
    • May 9, 2022 at 12:17 AM
    NO
    As user pdl pointed out, DCS would be the easiest way to do this. It looks like you have a CR-15 collaborative robot, and unless I'm mistaken that should require the DCS option?
    Here is a quick example Joint Position Check (Joint Limit) I set up in DCS that should be what you are looking for:
    Ignore the "Invalid Axis is selected" message. I whipped this up in a roboguide cell with a SCARA in it. Also, note that I am using the AUTO mode SSI to disable this joint position check, meaning it will only limit the robot in T1/T2 mode.
    If you somehow don't have DCS, or really want this to run in a BG program, you could use the SOP Teach pendant enabled output status, along with constantly checking the robot JPOS against a range of limit values. If the robot joint 5/6 pos is outside your limit, through a UALM. This would be quick, dirty, and not very fast but it would probably also work for you.
  • HawkME
    568
    3,268
    • May 9, 2022 at 7:11 PM
    I don't think you can use JPOS or UALM in BGLogic. But you could monitor the system variables for the current joint angles and if they are beyond some limit then drop out the UI Hold signal.
  • shriraj lonkar
    54
    • May 9, 2022 at 7:54 PM
    • #11
    Quote from HawkME
    How can I write the program for this can you elaborate
  • HawkME
    568
    3,268
    • May 10, 2022 at 3:23 AM
    • #12
    Those issues have been discussed on this forum before. Search for $SCR_GRP[1].$MCH_ANG
    Also read up on UI signals. They can be mapped to flags which allows you to easily control them in BG Logic.
  • Doctor_C
    33
    198
    • May 10, 2022 at 4:20 PM
    • #13
    You have DCS, so you can utilize this one. DCS position check, Target model collision
    This looks at the robot Bubbles versus the tool model. BIG thing is don't let the tool bubbles overlap the robot bubble when you create your tool model. Works really well
  • shriraj lonkar
    54
    • May 10, 2022 at 5:03 PM
    • #14
    Quote from Doctor_C
    [attach='34303','none','false'][/atta
    due to the weight issue, I can not use this manipulator as a cobot right now I am using it as a robot
    our part weight is 13.80 kg its Connecting Rod(CONROD)
    its execute the auto pay load weight in motion and DCS
    but whenever I am trying to run it in auto external mode (PLC Master and Robot Slave)
    It shows the weight is over load error or force monitoring error
    we also designed the gripper such as the CG of the part is in optimum position also cross-checked with Fanuc DATA SHEET excel. Fanuc also verified that this is the okay condition bus still we need to check whether the manipulator is in fault condition or not
    that's why I am using the NSI(non-safety input) to avoid the force monitoring input so the robot could run in an auto external mode without giving an force monitoring input
  • verove
    73
    • May 13, 2022 at 3:03 PM
    • Best Answer
    • #15
    Disabling the force monitor does not affect whether you can use DCS Position Check with a Target User Model.
    You can still use all the other functions of the DCS menu, even if you're not using the collaborative functions for the robot.
    In fact, the DCS Target User Model is designed to prevent exactly what you're looking for.
  • bg logic
  • FANUC SOFT LIMIT
  • SOFT LIMIT TO AXIS