Ethernet/IP Safety (CIP Safety)
  • Napster_matta
  • April 27, 2022 at 2:24 PM
  • Napster_matta
    7
    32
    Hi Guys,
    We usually hardwire safety signals (Dual Channel) from R30iB Plus to Allen Bradley GaurdLogix PLC.
    Due to the lack of availability of PLCs and components :frowning_face: , we are forced to look into other ways of doing safety.
    Has anyone worked EhternetIP Safety Option on Fanuc robots?
    If my understanding is correct, safety over EthernetIP will eliminate the need to hardwire safety signals between PLC and Fanuc controller. Is this correct?
    are there any limitations to using EthernetIP safety and IO Signals on a single ethernet cable?
    Thanks In advance.
    Kind Regards
  • HawkME
    570
    3,269
    • April 27, 2022 at 8:00 PM
    Yes, it will eliminate needing to hardwire safety signals.
    Yes there is a limitation to doing both Safety and Standard IO on the same cable. It is supposed to be possible to do so on a single cable by utilizing a DNS setup on the Robot. Otherwise you can separate them with Safety on 1 Ethernet port and standard IO on another with 2 separate IP addresses. Details are in the manual.
  • DS186
    200
    1,075
    • April 27, 2022 at 10:42 PM
    CIP safety ist a certified extension of the standard (non-safe) CIP capabilities for CIP based networks (e.g. Ethernet/IP).
    Standard and safety communication is all going through the same physical connection. It ist only one ethernet cable required.
  • Napster_matta
    7
    32
    • April 28, 2022 at 9:34 AM
    Quote from HawkME
    Quote from DS186
    Hi Guys,
    Thanks for the reply.
    I read the manual and we'll be separating safety and Standard IO.
    Do you guys have any recommendations on the byte size for safety? In the manual, it shows an example with 2 bytes. Is this enough?
    Thanks for your help.
  • HawkME
    570
    3,269
    • April 28, 2022 at 2:07 PM
    I think that's enough for the safety side.
  • jorge_oct8
    • August 2, 2023 at 6:33 PM
    ¡ Hola
    podría ayudarme con el mismo problema, dividir los 2 puertos ethernet usando el CIP
    o sabes donde puedo encontrar ese manual de configuracion
  • HawkME
    570
    3,269
    • August 2, 2023 at 6:56 PM
    Give us some details on your setup, what you have tried, what error and issues you are having.
  • jorge_oct8
    • August 2, 2023 at 7:17 PM
    configure standard Ethernet IP. I can already see it, it is in runing
    but I can not partition the ports, in standard and security
    menu > configure > I/O > ethernt IP > F3
    in the safety I/F status option : IDLE
    I want to know how to change the IDLE to Running
  • Alangt63
    • February 27, 2025 at 7:48 PM
    have you guys seen scenarios where the robot looses ethernet every so often ? having some issues with the robot losing the ethernet and the safety bits drop because of it and stops the robot we have change the ethernet card on the robot cab 30ib and change the ethernet cable going to the controller but still happens it can run for hours without doing it and sometimes it does it every so many minutes
  • jstolaruk
    16
    189
    • February 28, 2025 at 2:05 PM
    Yes. We usually find its a questionable cable. But not always.
    A couple of times, it was the PLC sensing a dropped Estop from the robot. I put TOF timers on the estop bit and the problem disappeared. Its never been the robot detecting an estop from the PLC so I suspected something on the PLC or Stratix switch side.
    This is with the default safety RPIs set to 10ms from the robot and 20ms to the robot. Its possible changing these could help.
    All of these changes still satisfied the risk assessment.
  • Alangt63
    • February 28, 2025 at 3:08 PM
    • #11
    jstolaruk I can try it. but having an e stop signal from the plc to the robot don't make sence that it would loose communication because of an e stop. If I was to make the RPI what would you suggest I change them to?
    Edited once, last by Alangt63 (February 28, 2025 at 4:03 PM).
  • jstolaruk
    16
    189
    • March 3, 2025 at 4:44 PM
    • #12
    Quote from Alangt63
    Something longer that won't impact the risk assessment.
Similar Threads
  • Ethernet/IP Safety (EIP-Safe), R-30iB Plus
    • ddtdustin
    • February 21, 2019 at 8:55 PM
    • Fanuc Robot Forum
  • KRC4 8.6.5 Ethernet/IP 4.1.3 With Schneider M241 PLC communication
    • Skarin
    • March 10, 2022 at 9:44 PM
    • KUKA Robot Forum
  • Multiple robots per cell and safety
    • Duranthas
    • April 14, 2022 at 2:01 PM
    • Fanuc Robot Forum
  • Robot CIP Safety Comm Timing out
    • rhorridle
    • February 14, 2022 at 12:21 PM
    • Fanuc Robot Forum
  • Safety Rated Signals Over Profibus?
    • Nation
    • June 4, 2020 at 1:48 PM
    • Fanuc Robot Forum
  • Resetting safety on krc4
    • AutoCamden2020
    • March 11, 2020 at 12:43 PM
    • KUKA Robot Forum
  • Discrete safety interface X11 - Ethernet safety interface X66 help
    • Fabian Munoz
    • April 12, 2019 at 2:48 PM
    • KUKA Robot Forum
  • Controller Safety Wiring Needs
    • ESIELI
    • July 11, 2018 at 7:36 PM
    • Fanuc Robot Forum
  • ethernet/ip
  • Allen Bradley
  • CIP Safey
  • Guardlogix