    Hey guys,
    I have a R-30-iB Compact Plus controller (software version V9.30P/20) and the Hot Start done signal from the System/Config menu is not working. I have tried every start mode, several power cycles of the controller, used different outputs, etc., but nothing helped. The signal never turns on. Did somebody of you experience the same behavior or do you have some tips what I can check and test?
    Regards
    Daniel
    Images
      • 19.75 kB
      • 649 × 282
      • 7
  • Erik Olsen
    59
    5
    192
    • March 22, 2022 at 6:50 PM
    Can a compact controller even perform a hot start? I thought the only way to power cycle them was with the controller breaker?
    DS186
    200
    1,075
    • March 22, 2022 at 7:19 PM
    You are right, but you can choose the hot start mode via FCTN > START MODE > HOT. After that, a manual power cycle is required.
    This is basically the same as with the Mate controller. I have tested it with a R-30iB Mate Plus controller. Configured the Hot Start done signal, manually turned the power off and on again and it worked as expected.
  • HawkME
    570
    3,269
    • March 23, 2022 at 12:42 AM
    Are you sure that DO is configured properly? And not used elsewhere in the program?
    DS186
    200
    1,075
    • March 23, 2022 at 6:52 AM
    I am pretty sure, because I have tested with 10 or 12 different DOs configured to different racks (102 and 48).
  • HawkME
    570
    3,269
    • March 23, 2022 at 6:56 PM
    Try rack 0 slot 0.
    DS186
    200
    1,075
    • March 24, 2022 at 7:52 AM
    Thanks HawkME, I will give it a try.
    DS186
    200
    1,075
    • March 24, 2022 at 11:18 PM
    The Hot Start done signal is now doing its job. The solution is the system variable $AUTOMODE_DO (which is the System/Config entry "Allow Force I/O in AUTO mode"). If it is TRUE the Hot Start done signal works, if FALSE, it does not work.
    Images
      • 10.63 kB
      • 636 × 109
      • 16
  • HawkME
    570
    3,269
    • March 24, 2022 at 11:41 PM
    Thanks for posting the solution! Could be helpful for others.