Hello, can you tell me how to set up data exchange between devices? The robot has an Ethernet/IP communication protocol. There is an LCCF_EnetScanner library, but I didn't figure out how to do it. New to communicating with the Fanuc robot. Thanks!
Fanuc R-30IB Mate Plus + Siemens 1516-3PN/DP
- coolvitaly
- Thread is marked as Resolved.
-
-
We need more details.
Which device shall communicate with which device or controller?
Where is the cp1516 installed?
Is the robot the controller or device?
At first you should read the Fanuc manual for Ethernet/ip
-
We need more details.
Which device shall communicate with which device or controller?
Where is the cp1516 installed?
Is the robot the controller or device?
At first you should read the Fanuc manual for Ethernet/ip
A robot with a controller. We need to establish communication so that the robot is a master. But this requires a PROFINET board. I read on the forums that the SIEMENS controller can be configured as a scanner, and in the documentation there is an example for CPU 1516+ET200+CPU1215
-
We need to establish communication so that the robot is a master
Communication always needs two partner, what is the device?
-
S7-1500 and S7-1200 can be operated as Scanner and Adapter mode with Ethernet/IP
Just read related manuals from Siemens and Fanuc for Ethernet/IP
-
S7-1500 and S7-1200 can be operated as Scanner and Adapter mode with Ethernet/IP
Just read related manuals from Siemens and Fanuc for Ethernet/IP
Yes, I have read this document. I thought maybe someone has already done this and there is an example