Positive decimal input using group / digital input from Allen Bradley PLC
  • jsd5
  • January 26, 2022 at 4:33 AM
  • jsd5
    18
    I'd like to transfer decimal numbers from an Allen Bradley PLC to Fanuc r30-ib controller.
    The numbers would be less than 200, but would need two decimal points, such as 100.01
    Is there an easy way to receive decimal numbers?
  • Go to Best Answer
  • neighbour1
    44
    405
    • January 26, 2022 at 10:25 AM
    Well... the easiest is to multiply by 100 (PLC side) and then divide by 100 (robot side).
    Then prepare a group with enough bits for numbers up to 20000 (=15 bits).
  • HawkME
    568
    3,268
    • January 29, 2022 at 3:35 PM
    • Best Answer
    Do you have Ethernet IP on the robot? If so you can use a MSG instruction on the PLC to write a real number to a register.
  • jsd5
    18
    • February 2, 2022 at 11:02 PM
    Quote from HawkME
    Yes I have Ethernet IP, I'll look into this
  • ethernet/ip
  • Allen Bradley
  • R30-iB
  • Decimal Data
  • Digital IO
  • Group Input
  • LR Mate 200iD