Error on reading/writing SYS-X44_EL6695
  • capital9
  • December 21, 2021 at 9:22 AM
  • capital9
    71
    Hi guys,
    I am working with KRC4 to KRC4 communication where I used EL6695 terminal bridge. The communication seems to be ok. Same amount of byte are exchanged from both side. There is clearly a good communication between them but problem is I am receiving a warning regarding byte mapping because of which the kuka robot can not go to automatic mode. I removed the communication and tested if the robot can go to automatic mode and it did go to Automatic mode.
    What can be the reason for this?
    What are the mandatory requirements for communication between Ethercat devices?
    i have attached some pictures in zip file please have a look at it. and tell me what can i do to get rid of this warnings?
    Files
    error byte mapping.zip 10.27 MB – 41 Downloads
  • capital9
    71
    • December 22, 2021 at 1:09 PM
    /////// SOLVED ///////
    Byte mapping errors were there because there were 3 signals which were automatically there after adding the device (EL66XX), the signal names are :
    ---SYNC inputs External device not connected
    ---SYNC inputs TxPDO state
    ---SYNC inputs TxPDO toggle
    when they were connected to input signal on the both side of ethercat device (which in my case were KRC4 both ways).
  • Bad_block
    95
    • December 22, 2021 at 2:08 PM
    I have alredy done this comunication with Backhoff Industrial PC, now I Know it works with 2 KRC4, thankyou tell us.
    Sulivan - Automatikbr.com
    Robotics Technician Brazil.
  • capital9
    71
    • December 22, 2021 at 2:13 PM
    yeah it works because i think both the system are Ethercat based.
  • JKPNEWBIE
    75
    • September 22, 2022 at 2:17 PM
    Hi all ,
    iam getting same problem
    i have only one robot and iam using el6695 from beckhoff not kuka one el6695-1001
    kss 8.6.8
    kr10 r 1100
    please do advice
  • capital9
    71
    • September 22, 2022 at 3:02 PM
    JKPNEWBIE check that above message try to disconnect bridge terminal (EL6695) from whole project software and hardware side, then step by step connect it then check if you get that input that are mentioned above, they are supposed to be connected to input as well which will eventually clear the error.
  • JKPNEWBIE
    75
    • September 22, 2022 at 4:35 PM
    Hi
    capital9
    Thanks for the advice.i have tried same thing but still I have the error
  • capital9
    71
    • September 23, 2022 at 10:31 AM
    JKPNEWBIE have you checked all the setting processes are ok, are there equal amount of bits, bytes, words defined. how about the right version of bridge terminals? there should be primary and secondary sides, have you defined them in right way? what is the communication happenning between ? KRC4 to KRC4 or something else?
    looks like primary side is not working, check the secondary side as well if it is working. also check the inputs 201 202 and 203 if there is any signal comming or going through.
  • JKPNEWBIE
    75
    • September 23, 2022 at 12:51 PM
    Hi capital9
    Bridge terminal is version 4.0 from beckhoff
    Communication is from beckhoff cx 5230 PLC and krc4
    Krc4 side is primary and PLC side is secondary
  • capital9
    71
    • September 23, 2022 at 1:08 PM
    JKPNEWBIE
    so you have to use twincat for that and connect them together, you have to do the settings in the twincat as well have you done that?
  • Beckhoff
  • EL6695