YRC1000 ALARM 4762: M-SAF GENERAL INPUT DIAG. ERROR2
  • Hi,
    I have a problem with YRC1000 controler every now and this ALARM 4762 apears with [0000_0000_1000_0000].
    Somtimes ther is a second alarm ALARM 4772 also with [0000_0000_1000_0000].
    Sometimes it goes away after one reset, sometimes it stops robot every few minutes =O
    How can I know with which input theres a problem? From documentation its D09:XIN09. But which one is it physically in YRC1000 Controler?
    My guess its one of two IM-YE250/5-80P.
    Did anyone have similar problem?
    ASF01 and ASF02 was already replaced
  • Hi,
    I don't know about your wiring, how many terminal you use in the robot and how you connect power supply for input/outputs.
    In the Alarms that you have, see the binary codes from right not left. The alarm show D08:XIN08 not D09:XIN09.
    Did you connect any thing to A6 and A13 pin on the CN309?
  • 4762 M-SAF GENERAL INPUT DIAG. ERROR2
    An error is detected by ASF01 board in self diagnosis process of function safety general safety input signal of ASF02 board, ASU03 unit.
    The meaning of each sub code is as follows:
    D01: XIN01
    D02: XIN02
    D03: XIN03
    D04: XIN04
    D05: XIN05
    D06: XIN06
    D07: XIN07
    D08: XIN08
    D09: XIN09
    D10: XIN10
    D11: XIN11
    D12: XIN12
    D13: XIN13
    D14: XIN14
    D15: XIN15
    D16: XIN16
    Connection failure
    (1) Reset the alarm.
    (2) If the alarm occurs again, check the connection and inserting state of the following cables and connectors. ·IM-YE250/5-80P terminal board
    ·ASF02, ASU03 - IM-YE250/5-80P terminal board cable
    ·Check connectors of the connected outside devices of XIN signal line.
    4772
    M-SAF GENERAL OUTPUT DIAG. ERROR2
    An error is detected by ASF02 board, ASU03 unit in self diagnosis process of function safety general
    safety output signal.
    is as follows:
    D01: XOUT01
    D02: XOUT02
    D03: XOUT03
    D04: XOUT04
    D05: XOUT05
    D06: XOUT06
    D07: XOUT07
    D08: XOUT08
    D09: XOUT09
    D10: XOUT10
    D11: XOUT11
    D12: XOUT12
    D13: XOUT13
    D14: XOUT14
    D15: XOUT15
    D16: XOUT16
    Connection failure
    ·Cable continuity between ASF02 board and ASU03 unit, IM-YE250/5-80P terminal board.
    The location of the IM-YE250/5-80P varies. It could be mounted on the door farthest from the hinge or could be mounted in the tophat, if you have a tophat. Since the alarm is an input and an output, I'd start with are you using them?
    If there is wiring attached, where does the wiring go? What physical devices. These signals could be used in the Machine Safety Logic Circuits or in a Safety File. You'd have to dig to see what these are used for. It could be something simple like a timing issue and the timer needs to be bumped up. It could be a position was changed and is causing a timing issue.
  • Hi,
    I have two IM-YE250/5-80P.
    So it should be this input?