I have a LR-Mate 200iB 5P. It has been stored for half a dozen years and now trying to repurpose. It has a R-J3b controller. I could not find docs or manuals. The issue is that I cannot clear SRVO-218 Ext E-stop/Servo Disconnect. I have jumpered what I think are fence and ext estop pins in controller. Nothing works! Any help is appreciated.
SRVO-218 Ext E-Stop / Servo Disconnect
-
dmanczunski -
September 10, 2021 at 2:16 AM -
Thread is Unresolved
-
-
External emergency stop input - connect EES1-EES11 and EES2-EES21.
It is the same as SRVO-007, but in the mate controller you will get SRVO-218.
-
i have encountered this before. Turns out it was a broken tp cable which caused the error.
-
External emergency stop input - connect EES1-EES11 and EES2-EES21.
It is the same as SRVO-007, but in the mate controller you will get SRVO-218.
I think this is the right path to check first, likely the jumpers were removed when it was last in use and you have nothing connected there.