ProfiSafe F-Paremeters keep resetting

  • Hey folks. I'm trying to figure out an issue that I am having between my IRC5 controller and S7-1200 communicating through ProfiSafe. I have an error on the PLC for one of the safety IO modules, that I *think* is caused by the fact that the destination address in robot studio keeps resetting itself. On the PLC they are set to 2 and 3, and when I try to set them in robot studio, I will try to write the config, wait for the power up, and then when it powers up, both devices are set to 1 for the destination address. Any ideas?

  • Hey jrfall,


    I had the exact same issue with my last ABB robot (in 2019). When I remember correctly, the solution for me was exporting the IO config (or the SafeMove config?), searched the F-source and F-destination address and changed the values. After that, importing and transferring the config to the controller worked.