Linking a DO to a BG logic run state
  • SkyeFire
  • May 20, 2021 at 7:54 PM
  • SkyeFire
    1,060
    9,456
    So, time for the next thing I need help with.
    I have been handed a hardware configuration with a heater controlled by a DO, and a temperature sensor feeding a DI. The robot needs to play the part of a thermostat, regardless of what the robot's status is.
    The complicating factor is that I need to do an AND function -- I need to enable/disable the heater based on a Flag, so my BG program was basically:
    DO[1] = DI[1] AND F[1]
    Which worked fine, right up until I halted the BG program to do some work on a different section of it, while the DO was On. And stayed on, until the heater eventually blew a fuse.
    I thought I could fix this by using a PULSE on the DO instead of a simple output assignment, but even if I do a simple DO=PULSE 1.0Sec command in a BG program, the DO never turns on.
    I could perhaps use a Marker, but I would need to connect the Marker to something (system variable?) that would be tied to the run/halt state of the BG program.
    I know how I could fix this easily in other brands, but I'm wondering what the best solution is on a Fanuc.
  • Go to Best Answer
  • HawkME
    570
    3,269
    • May 20, 2021 at 11:13 PM
    There's probably a system variable that could tell you the status, but a simpler approach could be to separate that 1 line out to it's own separate BG Logic program.
  • SkyeFire
    1,060
    9,456
    • May 21, 2021 at 2:59 PM
    The BG was originally a 1-liner, but stopping it caused the blow fuse. What I'm looking for is some kind of insurance against someone manually stopping the BGL.
    I did consider creating a second BG program to monitor the first, but then I'd need a 3rd to monitor the 2nd, and a 4th to monitor the 3rd, and...
    On a KUKA, my usual trick to solve this was to use a short Pulse command inside the background loop. In KRL, this guaranteed that, if the task stopped or hung for any reason, the output would go False soon after. I'll admit, the fact that I couldn't do that with BG really caught me flat-footed.
  • HawkME
    570
    3,269
    • May 21, 2021 at 3:28 PM
    You could do that with an auto execute program. In system config set either a hot or cold start auto execute program.
    Make sure it has the motion groups masked out and add an infinite jump label.
    You may also need to set no pause and no busy lamp.
  • HawkME
    570
    3,269
    • May 21, 2021 at 4:11 PM
    Ok, I found it.
    $MIX_BG[1].$STATUS
    the index is which BGlogic program, in this case 1.
    Status: 1= stopped, 2 = running in normal mode, 4 = running in high mode
    Now the question is what do you do with that information? If you want to monitor if it is stopped are you going to do so in another BG Logic program, or Auto Execute program, or maybe a system condition monitor?
  • jmd2777
    34
    193
    • May 21, 2021 at 6:05 PM
    A hardware solution could be a watchdog relay. That type of relay output remains on as long as the input toggles at a certain rate. So you would have to turn the DO on and off in a BG Logic program. If the BG Logic program is stopped, then the relay will turn off.
    DS186
    200
    1,075
    • May 22, 2021 at 9:44 PM
    Quote from HawkME
    Ok, I found it.
    $MIX_BG[1].$STATUS
    I normally check the status of my BG logic tasks in the initialization routine at the beginning of my main programs.
    If the mode of one or more BG logic tasks is stop, the program will be aborted. In this case, I send an error message which tells the operator to start the BG logic task.
  • SkyeFire
    1,060
    9,456
    • May 24, 2021 at 6:14 PM
    Quote from HawkME
    KAREL or TP? I've been experimenting with a TP program in the Auto Execute setting, but it never seems to run. Even if I remove the internal loop structure and just have it set a DO as evidence that it ran once, I don't get the DO.
    I set the boot program to BUSY_LAMP_OFF=1, ABORT_REQUEST and PAUSE_REQUEST=0, and set the Groups to *. No dice.
    I was hoping to avoid using KAREL on this project, but I may be stuck.
    Quote from HawkME
    Time for my next n00b question: what's a system condition monitor?
  • SkyeFire
    1,060
    9,456
    • May 24, 2021 at 7:02 PM
    Quote from SkyeFire
    Well, this is interesting. I've done some more experimenting with an Auto Exec TP program, and things are... odd.
    If I put a simple DO=ON into the program, it works -- on reboot, the DO is on. If I put a loop into the program, however, that loop never seems to execute. So I tried:
    WAIT 10.00 (sec)
    DO[623]=ON
    LBL[10]
    DO[624] = PULSE,1.0sec
    WAIT 0.1(sec)
    IF (!F[621]), JMP LBL[10]
    DO[623]=OFF
    If I turn off DO623, and reboot the robot, DO 623 gets turned on, and stays on, so the first part of the program is running. But it seems like the program aborts when it hits the loop structure -- DO 624 is never coming on.
    It's obviously not just skipping over the loop somehow, as the command to turn DO 623 back off never executes. And flipping F 621 has no effect, either, so it's not just stuck in the loop and failing to fire DO 624.
    Puzzling.
  • jmd2777
    34
    193
    • May 24, 2021 at 9:18 PM
    To help troubleshoot maybe you could put a longer wait such as 10 minutes. After rebooting, check the status of the program Menu->Next->Status. Check if your program is running or aborted.
    Also, use the Message instruction in several places in your code. This will allow you to write out some debug statements to the User screen. That can help to see what part of your code was executed.
  • jmd2777
    34
    193
    • May 24, 2021 at 9:19 PM
    • #11
    Is the robot configured for Hot Start or Cold Start? Make sure that you set the appropriate Auto Exec field based on if you are using Hot or Cold start.
  • SkyeFire
    1,060
    9,456
    • May 24, 2021 at 9:22 PM
    • #12
    Quote from jmd2777
    Did that already. The program doesn't show up at all, either running or aborted.
    The test program is in both Hot and Cold start. Which is a bit odd, b/c I only added it to Cold start, but it showed up under both after the first reboot. Strange....
  • jmd2777
    34
    193
    • May 24, 2021 at 9:30 PM
    • #13
    That is puzzling. I had an older controller that would not start the AutoExec program because the program name was longer than 8 characters. But it showed an error message in the System Log screen that said it could not find the specified program. Have you checked for any errors in the alarm screens?
  • HawkME
    570
    3,269
    • May 25, 2021 at 9:44 AM
    • #14
    Try changing the pulse 1.0 sec to just on. If that works then, switch it back to pulse 1.0 sec and change the wait to 1 sec.
  • SkyeFire
    1,060
    9,456
    • May 25, 2021 at 2:26 PM
    • #15
    Quote from jmd2777
    Yep, did that too. No program-execution errors, or I/O-access violations.
    Odder yet -- I built a virtual duplicate of the real robot in RoboGuide (so I could tinker after hours), and when I test-run the same auto-exec program, the explicit DO=ON never fires.
  • Nation
    Typical Robot Error
    553
    1,935
    • May 25, 2021 at 4:15 PM
    • #16
    I think the controller kills auto exec programs that don't complete after a certain amount of time.
    Edit: Found it:
    Try changing your auto exec program to run your test program.
    Code: Autoexec.tp
    : WAIT 10.00 (sec) ;
    : RUN BG_TEST ;
    Another option is a system level monitors that can be setup to run the moment the robot boots. Kind of the same problem though, they can be stopped and started via the status screen. Section 14.11.2 of the HanglingPro Manual goes over them
  • HawkME
    570
    3,269
    • May 25, 2021 at 6:48 PM
    • #17
    It can get it to work by disabling hot start and using it as a cold start autoexec program.
    Not sure why hot start doesn't work.
  • SkyeFire
    1,060
    9,456
    • May 25, 2021 at 9:58 PM
    • #18
    Quote from Nation
    Edit: Found it:
    That's good information to have. I don't think I can tamper with the Hot Start setting on this robot, since it's got a lot of "legacy standard" stuff required by the customer, but this suggests a reason why the startup program got aborted.
    Thing is... I did try having the "boot" program just RUN the background looping program, a couple times, without any luck. I'll have to try that again, a bit more scientifically, with this time limit in mind.
    Quote from Nation
    Ah! Another avenue to investigate! Thanks!
  • Lemster68
    301
    2,485
    Blog Articles
    7
    • May 25, 2021 at 10:11 PM
    • #19
    Quote from SkyeFire
    Big fly in the ointment is when the robot's status is powered off.
  • SkyeFire
    1,060
    9,456
    • May 25, 2021 at 10:34 PM
    • #20
    Quote from Lemster68
    That one at least isn't an issue -- I need the system to fail safe, and killing the robot power will allow all the relays to open, breaking the heater circuit and guaranteeing no thermal runaways.
    Unless the relays mechanically jam closed, but that could happen regardless of what kind of software protections I put in place.
Similar Threads
  • Kuka robot project and difficulties
    • Oatesy
    • December 17, 2020 at 5:59 AM
    • KUKA Robot Forum
  • BGLOGIC