Hello
KRC2
KR210 L150
KSS 5.2.14
E1 , E2 installed
system MIG/MAG welding since 2 years
I have the 246 error message :
SERVO BUS DISTURBANCE DSE **, NO BUFFERING AND
AUTOMATIC DATA STORAGE POSSIBLE
cause:
- Buffering is activated via the servo bus on the KPS. If communication
with the KPS is faulty, the buffering cannot be activated and switch--off
takes place immediately.
Remedy :
Re--establish communication with the KPS.
I made swapping with other cabinet changing KPS, ESC board , BUS cables with no solution.
What other ideas do you have ?
Thanks!